    Riser Tap

    Someone else is running the #600 riser. We are just running from the tap box to the panel( we are doing the tap). This happens at about 5 floors. I know of the Ilsco “port” type taps but couldn’t the piercing type be used to and eliminate the need to cut wires? Actually not sure the crimping type will work as I'm tapping #600 to #6 and they don't list that size range. Thanks.
    Attached Images Attached Images  
    Last edited by mstrlucky74; 04-16-19 at 03:04 PM.

  2. #2
    Join Date
    Jun 2010
    Location
    Bowmanville, Canada
    Posts
    103
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What is your question?

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,314
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yes insulation piercing taps will work if you can find them in the correct range.
    Last edited by infinity; 04-16-19 at 08:59 PM. Reason: Fixed Error
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,555
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    My other question. If you used a ported tap block you would have to cut the wire where your making the tap. If using insulation piercing you would not need to cut wire. Wouldn't you want to avoid cutting wire and jut pull wire point to point? Thanks

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,314
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    You either have to cut it or feed it through the tap if the hole is large enough to allow the insulated conductor to pass through.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,555
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    You either have to cut it or feed it through the tap if the hole is large enough to allow the insulated conductor to pass through.
    Your referring to these that the wire can be feed straight thru?

    https://commerce.ilsco.com/e2wShoppi...512:3100012872

  7. #7
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,314
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Your referring to these that the wire can be feed straight thru?

    https://commerce.ilsco.com/e2wShoppi...512:3100012872
    Yes if the hole is larger enough for the insulated conductor to pass through but since the riser will be installed by someone else that won't work for you. I would use insulation piercing taps if you cannot find the proper wire range you might need to make your tap conductors a bit larger.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  8. #8
    Join Date
    Jun 2010
    Location
    Bowmanville, Canada
    Posts
    103
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Does anyone have a link for the piercing tap connectors?

  9. #9
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,602
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  10. #10
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,555
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    Thanks