    Sub feed cable

    We are installing an outdoor disconnect for a 200 A service in a residential home. We will be running 4/0 AL from disconnect to the main panel inside. I have always ran 200 A sub feed cable ( I believe 4/0-4/0-4/0-2/0 AL)
    My question is..... why does the “ground” running from disconnect to panel need to be sized differently than our “earth grounds” (#6 Cu)??
    Can you site the NEC on this please? My helper asked me why and I did not have a definitive answer for him. I always assumed we sized equipment grounds on the size of the feeder cable but is the fourth wire in a sub feed an equipment ground? I am confused on this subject.
    Thank you in advance.

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,936
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yes, the EGC in the feeder is an equipment ground, and it is based on the size of the 200a main breaker.

    The rod GEC never needs to exceed #6 cu because that is considered to be the limit of earth conductivity.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  3. #3
    Join Date
    Mar 2018
    Location
    PA
    Posts
    58
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for the clarification on that.

  4. #4
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    1,144
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Because the ground running between the disconnect and panel is an “equipment ground” which needs to be sized to effectively carry a larger amount of current (to trip OCPD) than that of your “grounding electrode conductor” that lands on a ground rod. Earth/rod resistance no matter where you are on Earth is usually high enough to restrict the amount of current that the GEC will ever deliver.