    GFCI Breaker for Pool Lights

    Does the NEC 2017 require a gfci circuit breaker to be used to feed pool lighting circuit if the lighting system in using a NSI Industries TPX300 pool light transformer?

    The TPX300 is a step down transformer 120 primary / 14 v secondary.

    680.23 (A) 3. Says GFCI breakers to be used branch circuits supplying luminaires operating at a voltage greater than the low-voltage contact limit.

    Looking at the situation from the primary side one would say YES to the GFCI
    Looking it from the secondary side one would say NO.

    Advise

    Thanks

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,863
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    The primary side needs gfci protect however I have never seen gfci protection on the secondary side. We also gfci the line and that's all one can do.

    BTw, welcome to the forum
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,822
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I have never seen a GFCI made for LV. Further, because the LV secondary is prohibited from being grounded (IE it's floating), if it should fault to something there would be no risk.

    -Hal

  4. #4
    Join Date
    Mar 2007
    Location
    Valdosta, GA
    Posts
    4,546
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    The primary side needs gfci protect however I have never seen gfci protection on the secondary side. We also gfci the line and that's all one can do.

    BTw, welcome to the forum
    Does it ? The LV limit referred to in the article is 50v I believe; If you have less than that going to the shell of the pool I don’t believe a GFCI is required.


    Sent from my iPhone using Tapatalk
    Brought to you by Carl's Jr. ©

  5. #5
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,591
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hbiss View Post
    I have never seen a GFCI made for LV. Further, because the LV secondary is prohibited from being grounded (IE it's floating), if it should fault to something there would be no risk.

    -Hal
    interesting, was the intent on purpose?....~RJ~

  6. #6
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,822
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Good question because it doesn't only apply to pool LV wiring.

    -Hal

  7. #7
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,591
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hbiss View Post
    Good question because it doesn't only apply to pool LV wiring.

    -Hal
    hmmmm. well i have some thoughts on that, but would like to ask what yours are first Hal

    ~RJ~

  8. #8
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,822
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Only think I can think of is minimizing the shock hazard. 48V can give you a good tingle.

    -Hal

  9. #9
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,591
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I'm imagining a step potential applies for water, along with those immersed in it

    that said the older industrial ungrounded deltas w/impedance shunts (230.82-4) comes to mind

    one leg to ground was no thing....

    ~S~

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •