    Does the NEC 2017 require a gfci circuit breaker to be used to feed pool lighting circuit if the lighting system in using a NSI Industries TPX300 pool light transformer?

    The TPX300 is a step down transformer 120 primary / 14 v secondary.

    680.23 (A) 3. Says GFCI breakers to be used branch circuits supplying luminaires operating at a voltage greater than the low-voltage contact limit.

    Looking at the situation from the primary side one would say YES to the GFCI
    Looking it from the secondary side one would say NO.

    Advise

    Thanks

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,451
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    The primary side needs gfci protect however I have never seen gfci protection on the secondary side. We also gfci the line and that's all one can do.

    BTw, welcome to the forum
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,452
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I have never seen a GFCI made for LV. Further, because the LV secondary is prohibited from being grounded (IE it's floating), if it should fault to something there would be no risk.

    -Hal