    MCCB - Short time Setting - TCC - Clarification

    The attached is the TCC curve for a short time funtion of the trip unit does not show, at which of the current value it trips, though commit time and clear times are provided


    In the attached TCC, just for set band values, the trip times are mentioned. How can I find the appropriate current value?
    Attached Images Attached Images

  2. #2
    Join Date
    Aug 2008
    Location
    San Francisco
    Posts
    768
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The values of current are in multiples of LTPU, or trip unit sensor rating.
    I.E. for an 800A rated trip unit, if the STD setting is set on band 2 and the breaker is drawing 1600A (2X) then the trip time would be from 1.5 to 2.4 sec.