    Transformer Noise Levels

    A colleague just asked me whether there is an industry standard that governs (i.e., intends to limit) noise levels from transformers. His role is to establish criteria by which to evaluate proposals from contractors who wish to bid on the project. The transformer of interest is being replaced, and is on the order of 20 MVA. I don't have project drawings available, but my best guess is that there is a medium voltage primary and a 480/277V secondary.

    Any ideas? Is this in the NEMA world, or the IEEE world, or elsewhere?
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.

  2. #2
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,736
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    NEMA has a standard for dry type up to 1MVA https://www.nema.org/Standards/Secur...20-2014WMS.pdf

    Table 6 from this link has some liquid filled up to 3MVA too http://www.eaton.com/ecm/groups/publ.../ct_129982.pdf
    Last edited by ron; 04-17-19 at 03:15 PM.
    Ron

  3. #3
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,587
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    IEEE C57.136-2000 is for liquid filled power transformers over 500kVA and specifically addresses sound abatement requirements.