    Grounding dry type 120/208–277/480v transformers

    Have an inspector that says you must use grounding type bushing on conduits entering transformer.
    is this a new code requirement I’m not aware of because I have always used plastic bushings

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,541
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Unless there are concentric or eccentric KO's and it's over 250 volts to ground they are not required. The GEC in a metal raceway is a different story.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted