User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 12
Thread: CADWELD & PGE
  1. #1
    Join Date
    May 2010
    Inside the Beltway
    Posts
    674
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    CADWELD & PGE
    I was working on a job in NoCal where we'd be fed 3-ph by PGE.
    They required 2 grounds for the pad-mount transformer.
    Their "Green Book" specified the type of clamp.
    I wanted to CADWELD the wire to the rod. They didn't want to accept that and could not explain why.
    I did "when in Rome" and clamped the wire AND then CADWELDed it too.
    But I still wonder -- why wouldn't they want a welded connection?
  2. #2
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,632
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Depending on the size of the conductor, Cadwelds may have internal voids/pits that can reduce the cross-sectional area of the connection and reduce its effective ampacity. The phenomena can begin around #4 AWG. Truthfully, this isn't generally a serious problem with grounding electrode connections but it can be a big deal with some bonding connections.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2017 NEC unless otherwise noted.
  3. #3
    Join Date
    May 2010
    Inside the Beltway
    Posts
    674
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks; I'd never heard of such.
  4. #4
    Join Date
    Apr 2007
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    7,112
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Open Neutral View Post
    more and more, i've seen specifications that want a compression connection,
    and they want to be able to see the die number witness on the fitting.
    in other words, burndy 12 ton press, and burndy dies. not universal, which i think
    is a bunch of hooey, but it's 'cause the harbor freight crimpers that are metric, and
    don't get things stuck together well enough.
    it's been almost 10 years since i did a cadweld.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~
  5. #5
    Join Date
    May 2011
    Posts
    5,433
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Seems obvious that the only explanation they felt was needed was 'it's not in our book'.
  6. #6
    Join Date
    Apr 2007
    Posts
    7,112
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    bob always comes up with amazing stuff.
    anywhere in article 500, that is who i'd listen to, if i needed an answer...
    well, one that was correct, that is.
  7. #7
    Join Date
    Dec 2008
    Posts
    617
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    IEEE 142/2007 Green Book
    4.3.3 Connecting to electrodes
    Connections to electrodes are usually made by one of several means: mechanical, fusing,
    or compression. The first of these methods, mechanical fittings, is best suited for making
    connections to ground as the fittings are often easily disconnected, allowing for periodic
    ground-to-earth measurements.
  8. #8
    Join Date
    May 2010
    Inside the Beltway
    Posts
    674
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    My perspective is the biggest threat to a good ground is a corroded connection, 20 years after the fact. That's why I preferred welded connections.
    I'm puzzled that the standards folks are seemingly unconcerned about that.
  9. #9
    Join Date
    Mar 2013
    California, USA
    Posts
    82
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Are there not also concerns about toxic byproducts resulting from the process of exorthermic processes such as cadwelding?
  10. #10
    Join Date
    Jul 2005
    (44.057116, -123.103394)
    Posts
    536
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Julius Right View Post
    Easily disconnected, allowing for periodic
    ground-to-earth measurements[
    Comments based on 2017 NEC unless otherwise noted.
Tags for this Thread