    I was working on a job in NoCal where we'd be fed 3-ph by PGE.
    They required 2 grounds for the pad-mount transformer.

    Their "Green Book" specified the type of clamp.

    I wanted to CADWELD the wire to the rod. They didn't want to accept that and could not explain why.

    I did "when in Rome" and clamped the wire AND then CADWELDed it too.

    But I still wonder -- why wouldn't they want a welded connection?

  2. #2
    Join Date
    Apr 2004
    Location
    Mission Viejo, CA
    Posts
    5,632
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Depending on the size of the conductor, Cadwelds may have internal voids/pits that can reduce the cross-sectional area of the connection and reduce its effective ampacity. The phenomena can begin around #4 AWG. Truthfully, this isn't generally a serious problem with grounding electrode connections but it can be a big deal with some bonding connections.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2017 NEC unless otherwise noted.

  3. #3
    Join Date
    May 2010
    Location
    Inside the Beltway
    Posts
    674
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks; I'd never heard of such.

  4. #4
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    7,115
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Open Neutral View Post
    I was working on a job in NoCal where we'd be fed 3-ph by PGE.
    They required 2 grounds for the pad-mount transformer.

    Their "Green Book" specified the type of clamp.

    I wanted to CADWELD the wire to the rod. They didn't want to accept that and could not explain why.

    I did "when in Rome" and clamped the wire AND then CADWELDed it too.

    But I still wonder -- why wouldn't they want a welded connection?
    more and more, i've seen specifications that want a compression connection,
    and they want to be able to see the die number witness on the fitting.

    in other words, burndy 12 ton press, and burndy dies. not universal, which i think
    is a bunch of hooey, but it's 'cause the harbor freight crimpers that are metric, and
    don't get things stuck together well enough.

    it's been almost 10 years since i did a cadweld.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  5. #5
    Join Date
    May 2011
    Posts
    5,441
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Open Neutral View Post
    ...

    Their "Green Book" specified the type of clamp.

    I wanted to CADWELD the wire to the rod. They didn't want to accept that and could not explain why.
    ...
    Seems obvious that the only explanation they felt was needed was 'it's not in our book'.

  6. #6
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    7,115
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Open Neutral View Post
    Thanks; I'd never heard of such.
    bob always comes up with amazing stuff.
    anywhere in article 500, that is who i'd listen to, if i needed an answer...
    well, one that was correct, that is.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  7. #7
    Join Date
    Dec 2008
    Posts
    619
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    IEEE 142/2007 Green Book
    4.3.3 Connecting to electrodes
    Connections to electrodes are usually made by one of several means: mechanical, fusing,
    or compression. The first of these methods, mechanical fittings, is best suited for making
    connections to ground as the fittings are often easily disconnected, allowing for periodic
    ground-to-earth measurements.

  8. #8
    Join Date
    May 2010
    Location
    Inside the Beltway
    Posts
    674
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    My perspective is the biggest threat to a good ground is a corroded connection, 20 years after the fact. That's why I preferred welded connections.

    I'm puzzled that the standards folks are seemingly unconcerned about that.

  9. #9
    Join Date
    Mar 2013
    Location
    California, USA
    Posts
    82
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Are there not also concerns about toxic byproducts resulting from the process of exorthermic processes such as cadwelding?

  10. #10
    Join Date
    Jul 2005
    Location
    (44.057116, -123.103394)
    Posts
    540
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Julius Right View Post
    IEEE 142/2007 Green Book
    4.3.3 Connecting to electrodes
    Connections to electrodes are usually made by one of several means: mechanical, fusing,
    or compression. The first of these methods, mechanical fittings, is best suited for making
    connections to ground as the fittings are often easily disconnected, allowing for periodic
    ground-to-earth measurements.
    Easily disconnected, allowing for periodic
    ground-to-earth measurements[