    Elevator Main Disconnect

    I am adding some lights and GFI's on an elevator shaft due to motor controller upgrade. The elevator inspector is asking me to change the existing disconnect which is a 3 phase fusible 240 volts disconnect to a Heavy Duty one. Any one heard about this requirement? Motor is 7 1/2 HP and will be reuse. Label amps says 20.5 @ 208 volts
    Miguel

    All things, therefore, that you want men to do to you, you also must likewise do to them

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,531
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    To me, the what-was-compliant-when-installed clause ought to apply.

    But, then, I'm inexperienced with elevator-specific installations, so . . .
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  3. #3
    Join Date
    Dec 2010
    Posts
    1,498
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The existing switch may not be horsepower rated.

    see https://forums.mikeholt.com/showthread.php?t=142331
    The more they overthink the plumbing, the easier it is to stop up the drain