User Tag List
Page 2 of 3 FirstFirst 1 2 3 LastLast
Results 11 to 20 of 21
Thread: Can i do this
  1. #11
    Join Date
    Mar 2003
    Vermont
    Posts
    2,517
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    2020 I believe is going to prohibit a N-G bond in the solar disco and require a supply side bonding jumper back to the main disco. It changed between the first and second draft.
    But I would say that under 2014 and any other code besides 2020, you can treat them like you would multiple service disconnects, if the AHJ doesn't have an opinion.
    Quote Originally Posted by BandGap1.1eV View Post
    Best practices dictate a N-G bond only at one location, the main service disconnect. While we design and treat the solar disconnect as a service disconnect, it's not considered a "service".
    Bond the solar EGC to the main service EGC at the service entrance but leave neutral unbonded in the PV disconnect.
    I'll guess this is the 705/230 quagmire we've been hearing about
    ~RJ~
  2. #12
    Join Date
    May 2011
    Posts
    5,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    ~RJ~
    They just can't seem to get it right. I thought the first draft was basically fine. And then just when they finally decided to clarify things in 705, the other CMP went ahead and changed 230.71 and created new confusion.
  3. #13
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    514
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I still was not able to find 2020 second draft found first draft though.
    What is the proabability that second draft would be modified into something different i.e third draft? Can they still do that?
    Sent from my SM-G935U using Tapatalk
  4. #14
    Join Date
    May 2011
    Posts
    5,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The second draft should be further down the page.
    2nd draft will not change in substance, only to fix errors.
  5. #15
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    514
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Is it made public? You have link?
  6. #16
    Join Date
    May 2011
    Posts
    5,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    http://submittals.nfpa.org/TerraView...&pubStatus=SDR
    You need to register with the NFPA website, which costs no money.
  7. #17
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    514
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ok. What article in second draft 230 or 690?
  8. #18
    Join Date
    May 2011
    Posts
    5,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    705.11
  9. #19
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    514
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    705.11
    Ok but 705.11(D) Grounding and Bonding from second draft apply to disconnecting means mentioned in 705.11(E). However 705.11(E) is about connections not about disconnecting means. No disconnecting means 705.11(E). Am I missing something?
  10. #20
    Join Date
    May 2011
    Posts
    5,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You're missing that (D) refers to (F), not (E).