    Can i do this

    Attached sketch has AC PV disco and Building Service Disco.

    The GEC from Building Service Disco go to building electrode system. The GEC from AC PV disco gets bonded to the building service disco GEC.

    Is the sketch allowable per NEC 2014?

    Sent from my SM-G935U using Tapatalk

  2. #2
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2017
    Posts
    5,261
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Your picture is upside down.
    If you aim at nothing, you will hit it every time!

  3. #3
    Join Date
    May 2011
    Posts
    5,307
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ask your AHJ. This stuff will remain very open to interpretation and preference until you get on the 2020 NEC.

  4. #4
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    499
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Attached sketch not upside down.

    AHJ is mute about this matter. Any thoughts, experience or opinions appreciated including what 2020 has to say post #1.

    Question is can I bond AC solar disco GEC with the GEC of building service disco as shown in sketch?



    Sent from my SM-G935U using Tapatalk
    Last edited by hhsting; 04-30-19 at 11:41 PM.

  5. #5
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,486
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    At first sniff i'm inclined towards all GEC's in any given structure bonded together

    ~RJ~

  6. #6
    Join Date
    May 2011
    Posts
    5,307
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    2020 I believe is going to prohibit a N-G bond in the solar disco and require a supply side bonding jumper back to the main disco. It changed between the first and second draft.

    But I would say that under 2014 and any other code besides 2020, you can treat them like you would multiple service disconnects, if the AHJ doesn't have an opinion.

  7. #7
    Join Date
    Mar 2017
    Location
    East Coast
    Posts
    17
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Best practices dictate a N-G bond only at one location, the main service disconnect. While we design and treat the solar disconnect as a service disconnect, it's not considered a "service".

    Bond the solar EGC to the main service EGC at the service entrance but leave neutral unbonded in the PV disconnect.

  8. #8
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    499
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by BandGap1.1eV View Post
    Best practices dictate a N-G bond only at one location, the main service disconnect. While we design and treat the solar disconnect as a service disconnect, it's not considered a "service".

    Bond the solar EGC to the main service EGC at the service entrance but leave neutral unbonded in the PV disconnect.
    You are saying something like the attached sketch?

    Sent from my SM-G935U using Tapatalk

  9. #9
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    499
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    2020 I believe is going to prohibit a N-G bond in the solar disco and require a supply side bonding jumper back to the main disco. It changed between the first and second draft.

    But I would say that under 2014 and any other code besides 2020, you can treat them like you would multiple service disconnects, if the AHJ doesn't have an opinion.
    Whwre can I find the latest 2020 draft?

    Sent from my SM-G935U using Tapatalk

  10. #10
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,692
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    Whwre can I find the latest 2020 draft?

    Sent from my SM-G935U using Tapatalk
    The NFPA website.