Thread: Wire size reduction for branch circuits

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Join Date
    May 2019
    Location
    Baltimore, Maryland, United States
    Posts
    1
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)

    Wire size reduction for branch circuits

    My company installed LED lights in a school. The branch circuit is a 20 amp breaker with 12-2 wire. We installed 40 watt LED panels and a ceiling sensor with 14-3 MC from the switch leg box. The inspector failed us do to the fact the breaker is 20 amp therefore all wire must be 12 gauge. The ceiling sensor only draws 3 amps and has 18 wire hooked up internally. I referenced 240.5 (B)(2) witch states 14 can be used as fixture wire on a 20 amp breaker, but also went to table 402.3 and THWN is no listed. Is there any other code I should reference?
    Thanks all

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,730
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    The reference is that the inspector is correct. The sensor is part of the branch circuit not part of the fixture wiring so it must be 12 awg, IMO @D_Norris
    Last edited by Dennis Alwon; 05-01-19 at 05:37 PM.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Jun 2008
    Location
    Dallas, Tx
    Posts
    595
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by D_Norris View Post
    My company installed LED lights in a school. The branch circuit is a 20 amp breaker with 12-2 wire. We installed 40 watt LED panels and a ceiling sensor with 14-3 MC from the switch leg box. The inspector failed us do to the fact the breaker is 20 amp therefore all wire must be 12 gauge. The ceiling sensor only draws 3 amps and has 18 wire hooked up internally. I referenced 240.5 (B)(2) witch states 14 can be used as [Red]fixture wire on a 20 amp breaker, [Red]but also went to table 402.3 and THWN is no listed. Is there any other code I should reference?
    Thanks all
    Fixture Wire is the wire that is located on the inside of light fixtures. The Branch Circuit wiring is the wiring from the breaker to the outlet box.

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,329
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I agree, the #14 conductors are part of the branch circuit and must be a minimum of 20 amps unless you want to install 15 amp circuit breakers.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,748
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by xformer View Post
    Fixture Wire is the wire that is located on the inside of light fixtures. The Branch Circuit wiring is the wiring from the breaker to the outlet box.
    But what is the wire in the whip of a troffer? I always thought that was "fixture wire", as I dont see how it could be so small if it isnt.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,329
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    But what is the wire in the whip of a troffer? I always thought that was "fixture wire", as I dont see how it could be so small if it isnt.

    That would be a fixture tap and fall under 402.5 and 240.5(B)(2).
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #7
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    24,137
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    That would be a fixture tap and fall under 402.5 and 240.5(B)(2).
    And 240.5(B)(2) requires the use of fixture wire. Building wire of the same size is not permitted for that application. The only permitted wire types for that application are found in Table 402.3.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  8. #8
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,314
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    And 240.5(B)(2) requires the use of fixture wire. Building wire of the same size is not permitted for that application. The only permitted wire types for that application are found in Table 402.3.
    I don't see it requiring fixture taps to be fixture wire, it simply states allowable sizes to be used with different branch circuit ratings.

    410.117(C) allows any conductor type with suitable temp rating for the application to be used as a fixture tap, though that section applies to flush and recessed luminaires.

    410.62 (cord connected luminaires)also allows, with conditions, the use of smaller conductors than the branch circuit conductors.
    I live for today, I'm just a day behind.

  9. #9
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,692
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    But what is the wire in the whip of a troffer? I always thought that was "fixture wire", as I dont see how it could be so small if it isnt.
    If it is part of the fixture and its listing it is not under the NEC.

    Roger
    Moderator

  10. #10
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,908
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Wire from remote ballast can be #14, #16 depending on distance.
    It's considered part of the fixture. Or was code could have changed from the last time I did any work.