User Tag List
Results 1 to 3 of 3
Thread: Installing Switchboard Loads - Outage Necessary?
  1. #1
    Join Date
    Sep 2015
    Iowa City, Iowa
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hello all. I am creating an outage schedule for a construction project at a facility and was wondering if it is necessary to disconnect power to a new switchboard in order to install cables feeding several motor loads, or if this work can be done by simply opening the affected feeder breakers?
    Thank you for your time.
    +++Da Big Mek+++
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    17,752
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The short answer is the power needs to be shut down in accordance with OSHA and NFPA 70E, the long answer involves "hot work" permits, PPE, and a reason that the equipment can not be shut down.
    Roger
    Join Date
    Sep 2015
    Iowa City, Iowa
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for the help!
    +++Da Big Mek+++