    Either way (500 or 600 kcm) you need a 1/0 grounding electrode conductor.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  2. #12
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,742
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    I would definite ask the inspector why you must use a single 400 amp panel. That will cost twice as much as 2-200 amp panels
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #13
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,376
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I would guess that the 2-200 amps panels are not grouped together, hence the requirement for a main.