    400 amp service grounding

    I am bidding my first commercial job and i know that i need to run #2 copper for my 400 amp service. I never ran grounding for a 400 amp service. what is the recommeded way to attach to ground rods and water line? thank you
    Last edited by CharlesLindell; 05-06-19 at 12:59 AM.

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,430
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Water line uses a typical pipe ground clamp, and rods a typical rod clamp:

    Click image for larger version. 

Name:	81WV9uiC35L._SX466_.jpg 
Views:	41 
Size:	33.9 KB 
ID:	22901 Click image for larger version. 

Name:	031857491635.jpg 
Views:	42 
Size:	101.1 KB 
ID:	22902


    Maybe I don't understand the question?

    By the way, the wire to the rods never needs to exceed #6 cu.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,728
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by CharlesLindell View Post
    I am bidding my first commercial job and i know that i need to run #2 copper for my 400 amp service. I never ran grounding for a 400 amp service. what is the recommeded way to attach to ground rods and water line? thank you
    I assume you have 2-200 amp panels instead of one 400 amp panel. I also assume you have a CT cabinet. If so we run the #2 and the #6 to the cabinet
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,329
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by CharlesLindell View Post
    I am bidding my first commercial job and i know that i need to run #2 copper for my 400 amp service. I never ran grounding for a 400 amp service. what is the recommeded way to attach to ground rods and water line? thank you
    Do you have a single 400 amp service disconnect? What size service entrance conductors?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    3,090
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post

    By the way, the wire to the rods never needs to exceed #6 cu.
    By code, but more often than not I see Electrical Engineer's require 250.66 size ground throughout.


    I know what I don't know, and I know where to go to find it!

  6. #6
    Join Date
    Dec 2018
    Location
    Pittsburgh, Pennsylvania, USA
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I met up with the inspector at the job to go over things with him, since he will be inspecting it. He is requiring the 4oo amp service to have a 400 amp main panel, from there 2 200 amp sub panels. According to load, 500 cmils for service entrance is required. Meter is on the other side of wall. Service coming into the back of the panel.

  7. #7
    Join Date
    Feb 2013
    Location
    Aspen, Colo
    Posts
    2,046
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Master electrician should know there are many ways to do this, many are correct, & since this is your bid your choice. Seems to simple of a ? for an experienced tradesman.
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.

  8. #8
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,329
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by CharlesLindell View Post
    I met up with the inspector at the job to go over things with him, since he will be inspecting it. He is requiring the 4oo amp service to have a 400 amp main panel, from there 2 200 amp sub panels. According to load, 500 cmils for service entrance is required. Meter is on the other side of wall. Service coming into the back of the panel.

    So look at table 250.66 for 500 kcmil that will be the size for the water pipe. #6 is all that's required for a ground rod electrode.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  9. #9
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,430
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by CharlesLindell View Post
    I met up with the inspector at the job to go over things with him, since he will be inspecting it. He is requiring the 4oo amp service to have a 400 amp main panel, from there 2 200 amp sub panels. According to load, 500 cmils for service entrance is required. Meter is on the other side of wall. Service coming into the back of the panel.
    With double lugs on the meter load terminals, two 200a mains would also work. His single 400a main "requirement" is not reflected in the NEC.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  10. #10
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,748
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by CharlesLindell View Post
    I met up with the inspector at the job to go over things with him, since he will be inspecting it. He is requiring the 4oo amp service to have a 400 amp main panel, from there 2 200 amp sub panels. According to load, 500 cmils for service entrance is required. Meter is on the other side of wall. Service coming into the back of the panel.
    Quite a bit of $$ can be saved using 230.40 exception 2 and just 2 200 A MB panels. Not sure if for some specific aspect of the job that isnt feasible, or its a case of an inspector "wanting" something that he doesnt have the authority to demand....

    Also, 500 copper is too small for 400 amps, unless you can use the next size up rule to get from 380 to 400 (sometimes inspectors want load calcs if you use that provision).
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"