    230.40

    Attached sketch shows tenants A to tenants D in one floor building. Each tenant is spearsted by minimum 2hrs fire wall.

    Tenants A,B have service entrance conductors while tenants C,D have service entrance into utilty room of tenant D.

    Sketch shows blown detail of utlity room tenant D. There are two service disconnects fed from tenant D service entrance all grouped in utility room one feeding to tenant C panel and other tenant D panel.

    Tenants A,B service is allowable by Nec 2014 Article 230.40 exception number 1 while tenants C,D service is allowable by Nec 2014 Article 230.40 exception number 2.

    Can you have combination of Nec 2014 Article 230.40 exception number 1 and exception number 2 or just one exception is allowed in attached sketch?

    Sent from my SM-G935U using Tapatalk

  2. #2
    Join Date
    Jan 2007
    Posts
    4,134
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You sure do sketch a lot....

    JAP>

  3. #3
    Join Date
    Feb 2013
    Location
    Aspen, Colo
    Posts
    2,046
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I do not see where the NEC prohibits the use of exceptions -- you could use either throughout the building -so what would make either used (even in combination) a non compliant install?
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.

  4. #4
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    494
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Post #1 sketch Tenant D utility room blown up, would it still be NEC 2014 compliant if third meter was added feeding Landlord House Panel with main breaker in the utility room?

  5. #5
    Join Date
    Jun 2018
    Location
    Glen bunie, md, us
    Posts
    494
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    Post #1 sketch Tenant D utility room blown up, would it still be NEC 2014 compliant if third meter was added feeding Landlord House Panel with main breaker in the utility room?
    Any input from code experts appreciated.

    Sent from my SM-G935U using Tapatalk

  6. #6
    Join Date
    Jul 2005
    Location
    (44.057116, -123.103394)
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    230.70(A)(1)

    Seems like 2014 230.70(A)(1) would not be met as it shows the service conductors traveling a distance thru the building. Tenant C does not have access to service disconnect? 2014 230.72(C)
    Also do you have a load calc for the new and existing panels?