Thread: NEC 250.53 [D] (2) ground rod connection location

  1. #1
    Join Date
    Nov 2016
    Location
    Kennewick
    Posts
    168
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    NEC 250.53 [D] (2) ground rod connection location

    I have a home that has a water pipe as the primary electrode. I’m installing two ground rods as supplementary and I have made the connection to lug tapped onto the CT can feeding the service. It is grounded by the grounded service entrance conductor. I got a correction where the inspector referenced 250.24 [D] but I feel that 250.53 [D](2) allows me to connect my supplemental electrodes this way. What is your opinion?


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    May 2011
    Posts
    5,300
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree with you. Specifically 250.53(D)(2)(4), if I understand your description accurately.

  3. #3
    Join Date
    Nov 2016
    Location
    Kennewick
    Posts
    168
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    I agree with you. Specifically 250.53(D)(2)(4), if I understand your description accurately.
    Exactly! I have now elevated my disagreement up the chain to the lead electrical inspections supervisor. He was agreeing with me but wanted to take it up the chain and make sure the chief electrical inspector was on board with this. I’m like but it’s in the NEC and there is no WAC to supersede it... but I’m not naive to the fact he has the ability to not accept a code because he has the power of the AHJ.


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,314
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    I agree with you. Specifically 250.53(D)(2)(4), if I understand your description accurately.
    I would cite that section too but what does "any grounded service enclosure" mean? Is the CT cabinet a service enclosure?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    May 2011
    Posts
    5,300
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    I would cite that section too but what does "any grounded service enclosure" mean? Is the CT cabinet a service enclosure?
    If it has service conductors in it then I think it is. The utility might not like the EC doing stuff in it, but NEC doesn't care about that.