    250.64(C) "GEC's shall be installed in one continuous length without a splice or joint except as permitted in (1) and (2)
      (1) Splicing shall be permitted only by irreversible compression-type  connectors listed as grounding and bonding equipment or by the  exothermic welding process.
    What's the reasoning behind the irreversible connectors requirement for the GEC? Is it to prevent tempering or to ensure proper surge current passage? Would a split bolt, acorn, or screw lug style connector work the same from a physics perspective? thanks
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    17,692
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by EBQ View Post
    Code:
    Any connector properly installed will perform it's purpose from a physics perspective however, an irreversible connection is supposed to be just that which is permanent.
    Roger
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,748
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Code:
    There is no reason. It's just one part of the continued over emphasis in the importance of grounding
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,314
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Which may not be as important as some want to think it is. Bonding is definitely important though.
    I live for today, I'm just a day behind.
  5. #5
    Join Date
    Feb 2003
    Illinois
    Posts
    24,137
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Because for some unknown reason CMP 5 seems to think that a GEC is more important than an EGC. It is my opinion that the EGC is far more important than the GEC.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  6. #6
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,331
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    I agree, the system would work just fine with no electrodes or GEC's as long as the main bonding jumper was in place.
    Rob
  7. #7
    Join Date
    May 2019
    Northeastern US
    Posts
    5
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Does the GES even do anything meaningful locally for surge currents? when service neutral already provides a lower resistance path to absorb excess voltage and is bonded to earth at the transformer.
    Other than bonding earth to metal to equalize potentials, what else does a GES accomplish?
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,314
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It just adds one more electrode to a large network of electrodes.
  9. #9
    Join Date
    May 2019
    Northeastern US
    Posts
    5
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    So it's really insurance for the whole, rather than the individual, at least as it relates to a surge.
  10. #10
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,314
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    mostly yes.