    250.50

    I have an inspector in Florida that is failing me because I'm not installing a single ground rod when ufer ground is present. He is telling me the way he interprets 250.50 is that Ufer and a ground rod is required

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,329
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    He's incorrect. A CEE is not required to be supplemented with another electrode. What did he cite as a code reference 250.50 isn't it?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,314
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree with Infinity.

    If citing 250.50, it starts off with: All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure..

    Ground rods are in part 5, but until you add one they are not present either. They are usually added when nothing else is available or if there is nothing else available to supplement a water pipe electrode, they are not required to be added in those situations just the most popular choice of what to add.