    I'm planning to install a 13.2 kV/ 480 Volt 2500 KVA transformer, 3000 Amp switchgear (480 V) and 6 VFD drive cabinets.
    1. 13.2 kV/ 480 Volt, 2500 KVA transformer will be located outside the manufacturing plant. This transformer will feed a 3000 Amp switchgear rated for 480 V.
    2. This switchgear has 6 breakers that will feed 6 drive cabinets. All 6 drive cabinets will be installed inside a MCC room.
    3. My question is regarding switchgear installation location. Is it acceptable to install this 3000 Amp switchgear inside MCC room or does it have to be installed in a separate switchgear room ? Please note that MCC room already has a Distribution Panel (DP) fed by another transformer/ switchgear. In addition, MCC room will have many drive cabinets. MCC room has additional free space available.
    4. Can you please confirm which NEC section is applicable for installation location of switchegar ? I want to know what NEC says for installing switchegar inside MCC room along with other distribution panel (powered by a different transformer source) and drive cabinets or the switchgear must be installed in a separate switchegar room ?
    Thanks !
  2. #2
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,604
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    As long as you maintain the required working clearance and access rules the NEC will allow the gear in the room (or almost anywhere)
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  3. #3
    Join Date
    Dec 2008
    Posts
    604
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    NEC 2017 ARTICLE 408 Switchboards, Switchgear, and Panelboards
    Part II. Switchboards and Switchgear [from Art.408.16]
    and Art.110 Part II. 1000 Volts, Nominal, or Less [from 110.26].
    Also Art.312.2 Damp and Wet Locations
    [and also as augie47 said]
  4. #4
    Join Date
    Feb 2013
    India
    Posts
    2,713
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If the breakers in the switchgear contain any insulating mineral oil, it is better to house the switchgear in a separate room then.