User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 12
Thread: Transformer Damage Curve
  1. #1
    Join Date
    Mar 2012
    Minneapolis, MN
    Posts
    262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I have question about the protection and coordination of the transformer. The time current curve of the primary fuse usually passes through the transformer damage curve, then why is it even required that the transformer damage curve should be plotted?
    If the curve of fuse on the primary side of transformer passes through the transformer damage curve, then will the secondary fuse be able to protect the transformer, or should an additional 50 relay be used in series with primary fuse? Thanks for help.
  2. #2
    Join Date
    Feb 2011
    Las Vegas, Nevcada, USA
    Posts
    108
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by timm333 View Post
    The correct TCC of the primary fuse shouldn’t intersect the damage curve, where are you getting this from?
  3. #3
    Join Date
    Mar 2012
    Minneapolis, MN
    Posts
    262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    In the SKM application guide at the link: http://www.skm.com/applicationguides22.html
    In the second paragraph under the heading: MV Transformer Fused Switch Feeder Unit:
    It says that "typically the fuse will cross the transformer damage curve".
  4. #4
    Join Date
    Feb 2003
    Wisconsin
    Posts
    10,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The primary fuse is often intended to remove the transformer from the system after it has failed (i.e. short circuit protection). Overload protection is usually provided the secondary protective device.
    this is why the NEC requires either the primary or the secondary, but not both, to not exceed 125% of the FLA.
    Just because you can, doesn't mean you should.
  5. #5
    Join Date
    Mar 2012
    Minneapolis, MN
    Posts
    262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The damage curve is regarding short circuit protection (not overload). So if the primary fuse curve (providing short circuit protection) crosses the damage curve, it would damage the transformer. I am trying to understand why they say it is acceptable for the primary fuse curve to cross the damage curve.
  6. #6
    Join Date
    Feb 2011
    Posts
    108
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Looking at the reference, I see what you are now talking about... The primary fuse TCC is intersecting the long-time region and is perfectly acceptable since they are utilizing a secondary protective device to cover the long-time (overload) region on the secondary windings. Note: you don’t get overloads due to the primary windings itself so it’s ok to implement that protection on the load side of the transformer. Both primary and secondary TCC’s are superimposed.
  7. #7
    Join Date
    Apr 2015
    IL
    Posts
    195
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Also I think what they're saying is that it's best to select a fuse that won't blow during TX inrush and cross the damage curve, rather than the opposite - a fuse that doesn't cross the damage curve, but blows on transformer inrush.
  8. #8
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    4,817
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There is no code requirement to plot the transformer damage curve. It is an industry practice to do it and show that you have selected a fuse or other protective device to do the best you can considering the application.
    Ron
  9. #9
    Join Date
    Mar 2012
    Minneapolis, MN
    Posts
    262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Xptpcrewx View Post
    The "long time region" which you have mentioned, is it of damage-curve or fuse-curve ?
    The top half of the damage curve is for thermal and the bottom half is for short circuit. Regarding the fuse curve, it does not have the thermal and short circuit regions like a breaker, but still I think the top part of the fuse curve would be for thermal and bottom half for short circuit.
  10. #10
    Join Date
    Feb 2011
    Posts
    108
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I am referring to the thermal region of the damage curve