    I wasn't talking about oil. Oil and gas fired equipment are two distinct things.

    NFPA 31, Standard for the Installation of Oil-Burning Equipment, 2001 Edition
    10.5 Operating Controls.
    10.5.1*
    Oil burners, other than oil stoves with integral tanks, shall be provided with some means for manually stopping the flow of oil to the burner. Such device or devices shall be placed in a readily accessible location at a safe distance from the burner.
    10.5.1.1
    For electrically powered appliances, the requirement of 10.5.1 shall be accomplished by an identified switch in the burner supply circuit, placed near the entrance to the room where the appliance is located.
    10.5.1.2
    For appliances that are not electrically powered, an identifiable valve in the oil supply line, operable from a location that can be reached without passing near the burner, shall be used.
    10.5.2
    An electrical service disconnect switch, arranged to stop and start the oil burner, shall be installed at the appliance. It shall be located so that it is within easy reach of the service technician for control of the oil burner while observing the flame.
    -Hal

  2. #12
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,337
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by RICK NAPIER View Post
    It's no longer in the IMC but NJ has put it back in.

    vi.Add new Section M1307.7 as follows:M1307.7Safety devices and controls. Oil burners, other than oil stoves with integral tanks, shallbe provided with means for manually stopping the flow of oil to the burner. Such device ordevices shall be placed in a readily accessible location a minimum of 10 feet from the burner.For electrically driven equipment, an identified switch in the burner supply circuit shall beprovided at the entrance to the room or area where the appliance is located or, for equipmentlocated in basements, the switch is required to be located at the top of stairs leading to theOfficial version to be obtained from Lexis Nexis, www.lexis.comPage 13 of 18N.J.A.C. 5:23-3.21basement. An identifiable valve in the oil supply line, operable from a location a minimum of 10feet from the burner, shall be used for other than electrically driven or controlled equipment.
    I was referring to gas burners, your code section seems to reference oil burners.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #13
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,712
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    As was I. However the OP did ask or was confused about both gas and oil. As long as @RICK NAPIER brought up oil it was a good opportunity to talk about what that requires.

    -Hal