    Recently had numerous outlets in a medical procedure area where plug tester was showing open ground. I had been asked to install gfi protected outlets as this is considered a "wet" area. Medical equip tech informed me that there is a "floating ground system" present. What is this? How does it work? Does it negate the need for GFCI protection of personnel?
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    17,689
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Sounds like an Isolated Power System, see 517.160. Is there a panelboard with a Line Isolation Monitor in the area?
    If it is an Isolated Power System your plug tester will show faults, the system does not have a neutral, it is 60v / 60v L-L. You do not need GFCI's on these systems.
    Roger
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,289
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by roger View Post
    Roger
    Yes, make sure it isn't one of these before proceeding with anything. GFCI could even be undesired here, there is a reason it is set up like it is, if that is what it is.