User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 12
Thread: Sizing loads to industrial machinery
  1. #1
    Join Date
    May 2019
    Rochester ny
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We have in our factory a trim press machine with a nameplate FLA of 192 amps at 460 v 3 phase. No resistive load, just a control plc and 2 servo motors. Avg draw using a clamp on meter is 10 to 15 amps. It is fed from a 30 amp breaker with #10 wire and we have not had any problems for the 8 years this machine has been running, 3 shifts , five days a week. I need to relocate this machine within our factory. I’m stumped at finding a code allowace for under sizing a load, even though experience shows 30amps is more than enough. I hate to install a 200 amp service unnecessarily,but i dont want to be violating any codes at the same time. Any help would be greatly appreciated.
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,753
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    I don't believe the nameplate is correct. What is the HP of the motor?
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Dec 2014
    CO
    Posts
    113
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Mark1990 View Post
    Maybe the poster meant 19.2 amps?
  4. #4
    Join Date
    May 2019
    Rochester ny
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A little more detail on the machine. The prints call out several options not installed, totaling 33hp. Motors that are utilized are 27.5 kw servo and a 7.2 kw servo, along with a 7.5 kva transformer, for some 120 v loads. Maybe the nameplate includes the never installed options? My main question is, does the code allow me to run a smaller feed than the nameplate calls for? I dont see this anywhere in article 670. Any help is appreciated . Thank you
  5. #5
    Join Date
    Feb 2016
    Illinois
    Posts
    1,431
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I think if the conductors are properly protected, you’re fine code-wise.
    I have had similar experiences. We had machine tools that were never loaded anywhere near capacity. A vertical turret lathe with an integral 100 A breaker that never drew more than 15A the way it was used. Not uncommon.
    We never downsized the conductors, however. We never knew what kind of work it would be asked to do next month!
  6. #6
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    25,531
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    With the history of operation you provided, I would just duplicate what you have, and sleep well.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  7. #7
    Join Date
    May 2019
    Rochester ny
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree that practically speaking as long as conductors are properly protected there is not a fire hazard etc. my main sticking point is if the job were to be audited by our fire insurance company or corporate for some reason I would like a code to reference that allowed a smaller than nameplate service. As everything I read in the code points to sizing the conductors and over current protection based on machine nameplate FLA.
  8. #8
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,770
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MrJLH View Post
    Got a letter/number punch set with a "." in it
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  9. #9
    Join Date
    Feb 2003
    Wisconsin
    Posts
    10,325
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I don't see a problem.
    NEC 2017
    670.3(A)(2) - nameplate must list the maximum possible overcurrent protective device.
    670.4(A) - The conductor sizing shall take into account the loads that will be connected at one time based on their duty cycle.670.4(C) the overcurrent device is sized to handle the full load current connected at one time.
    Just because you can, doesn't mean you should.
  10. #10
    Join Date
    Feb 2016
    Illinois
    Posts
    1,431
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jim dungar View Post
    NEC 2017
    And since it ran for 8 years without problems on a 30A ocpd, it will obviously handle the actual full load current.