User Tag List
Results 1 to 6 of 6
Thread: wireway fill
  1. #1
    Join Date
    Jul 2005
    Posts
    318
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    wireway fill
    I need to a wireway for 6 paralleled 4-600mcm looking to see if i did this right. I wanted to use a 12x12 wireway
    12x12x20%= 28.8 / .8676 or 600mcm wire= 33.1 meaning i can install 33-600mcm wires. So i can use 12x12 wireway? did i do this right?
  2. #2
    Join Date
    Jul 2015
    Wilmington, NC USA
    Posts
    671
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mannyb View Post
    Looks right to me.
    I'm assuming you are not going to splice in this wireway.
  3. #3
    Join Date
    Jul 2005
    Posts
    318
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by oldsparky52 View Post
    Looks right to me.
    no Sir we just need the wireway to extend wire into building. We want to use wireway as a chase or extention into a Switchboard. BTW You think we need to use bonding bushings to each and or all penetrations?? There will be 6 conduits for feed.
  4. #4
    Join Date
    Jul 2015
    Wilmington, NC USA
    Posts
    671
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If you are punching your own holes to the correct size, then no you don't need a bonding bushing. I would however use a bonding locknut (that's just me).
    What type conduit are you using?
    Where are you entering the wireway (at the ends only, at the top or bottom, or combination)?
  5. #5
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,936
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Are these service conductors or feeders? Voltage, concentric KO?
  6. #6
    Join Date
    Jul 2007
    Posts
    463
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    do electricians typically use power distribution blocks inside wireways or do they prefer to just splice the cables?