    Means/Method

    So if you had a job that allowed MC but spec says have to run conduit out of panel to first box( usually guys run a 20’ HR from panel to box) and you had the panel about 80’ away from this area and you had to run separate neutrals would you run separate 12/2 from leach receptacle to near panel or would you run conduit from panel to the area of these receptacles with all the circuits in one pipe run mc up from recept. to box?
    Attached Images Attached Images  

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    10,055
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I usually run EMT as far as I can, but because of the separate neutral requirement I would run as much mc as I could.
    If you don't think too good, don't think too much.

  3. #3
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,555
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ActionDave View Post
    I usually run EMT as far as I can, but because of the separate neutral requirement I would run as much mc as I could.
    Why would the separate neutral have you run MC instead? You could run a multiple neutral MC.
    Last edited by mstrlucky74; 05-14-19 at 11:26 AM.

  4. #4
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    10,055
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Back in the day you could get six 20A circuits in a 1/2" EMT. Now you can only get 4 and it's pain to splice.
    If you don't think too good, don't think too much.

  5. #5
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,555
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ActionDave View Post
    Back in the day you could get six 20A circuits in a 1/2" EMT. Now you can only get 4 and it's pain to splice.
    Understand but we can run MC directly into panel so we have to splice( transition from EMT to MC) no matter what.

  6. #6
    Join Date
    Feb 2018
    Location
    New Jersey
    Posts
    24
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A 1 inch emt conduit with 10awg to combat derating and even leaves room for a wire type egc

  7. #7
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    10,055
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Understand but we can run MC directly into panel so we have to splice( transition from EMT to MC) no matter what.
    Do what you want. I don't care.
    If you don't think too good, don't think too much.

  8. #8
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,555
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ActionDave View Post
    Do what you want. I don't care.

  9. #9
    Join Date
    Jul 2005
    Posts
    929
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Understand but we can run MC directly into panel so we have to splice( transition from EMT to MC) no matter what.
    What?.....you just said in the OP that the spec required you to run EMT out of the panel....

    once again.......you contradict yourself in a matter of three posts

  10. #10
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    10,055
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by cdslotz View Post
    What?.....you just said in the OP that the spec required you to run EMT out of the panel....

    once again.......you contradict yourself in a matter of three posts
    It was a typo. Lighten up.
    If you don't think too good, don't think too much.