    PVC in a pump room

    Can I run PVC on a pump room for the Service wire coming underground

    Sent from my SM-N960U using Tapatalk

  2. #2
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,229
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Do you have a local ordinance that says No?

    Is it subject to damage?

    A hazardous area?

    I can here.
    Tom
    TBLO

  3. #3
    Join Date
    Jul 2011
    Location
    Orlando, FL
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    No, I've always seen Ridgid, that's why I asked. I couldn't find anything that says otherwise.
    It's odd to me that they would quote a job with Ridgid when you can run PVC

    Sent from my SM-N960U using Tapatalk

  4. #4
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    680
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Alejandro View Post
    No, I've always seen Ridgid, that's why I asked. I couldn't find anything that says otherwise.
    It's odd to me that they would quote a job with Ridgid when you can run PVC

    Sent from my SM-N960U using Tapatalk
    Have you checked the PoCo requirements? They would have a say on this since it's their side of the meter.

    Is it their side of the meter? I assumed so when you said "Service wire coming underground" in the OP.

  5. #5
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,640
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by oldsparky52 View Post
    Have you checked the PoCo requirements? They would have a say on this since it's their side of the meter.

    Is it their side of the meter? I assumed so when you said "Service wire coming underground" in the OP.
    Probably not. Fire pump conductors are treated as service conductors no matter what.

  6. #6
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    680
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gadfly56 View Post
    Probably not. Fire pump conductors are treated as service conductors no matter what.
    OP said pump room, and the 1st thing that popped into my mind was something like a carwash, a fire pump never crossed my mind.