    The equivalent impedance of parallel feeds is lower than single feed. So fault current is more and so EGC to be big enough to carry the increased fault current without burning up.

  2. #12
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,081
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    I agree except for parallel runs where the ungrounded conductor is the sum of all the parallel sets so you could end up with the EGC's in each parallel raceway that are required to be larger than the condcutors within each raceway.
    My thought also.

    Can't say I have ever run into it, maybe if you decided to never use larger than the minimum requirement of 1/0 for your parallel sets and were running a 4000 amp circuit