User Tag List
Page 1 of 6 1 2 3 ... LastLast
Results 1 to 10 of 59
Thread: kitchen countertop recep spacing with large garden window
  1. #1
    Join Date
    May 2005
    Posts
    91
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hello all,
    Have a custom kitchen countertop passing through a five-foot-wide garden window with no backsplash, flat right through. No sink or cooktop, just work surface. How does one satisfy the spacing requirement for receps serving countertop, cut a face-up into quartz? Yikes!
  2. #2
    Join Date
    May 2005
    Posts
    91
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ahh got it.
    "A receptacle outlet must be installed for every kitchen and dining area counter wall space 12 inches or wider. Receptacles must be installed so that no point along the counter wall space is more than 24inches (2 feet), measured horizontally, from a receptacle outlet."
    Garden window width is not a section of wall space, not counted.
  3. #3
    Join Date
    Jun 2003
    Posts
    11,270
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by TimWA View Post
    ahh got it.
    I believe a window is counted as counter wall space. Floor to ceiling windows are counted as wall space in the rest of the home.
    That said, I don’t follow your description of a garden window.
    Tom
    TBLO
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,346
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    +1
    If the entire "wall" was glass it doesn't change any of the rules on spacing.
    Absence of a "wall" at this counter makes it an island or peninsula, where the rules do change.
    I live for today, I'm just a day behind.
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,346
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hello all,
    ahh got it.
    Face up is a no-no unless it is something listed for the purpose, but most of those designed to go into a counter are "pop up" type devices. Outlets just below the counter and in the front of the base cabinet may be acceptable, kind of an inspector call in this situation though. If your "window is less than 4 feet wide, a receptacle on each side of window is fine if there is no more than 4 feet between them.
  6. #6
    Join Date
    Jul 2007
    Iowegia
    Posts
    18,538
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hello all,
    Face-up in the c'top isn't allowed.
    You need to take a baseball bat, walk into the designer's office and beat the living daylights out of them for designing a kitchen that cannot comply with building codes. They need to learn there are codes that must be followed and quit laying out kitchens and such based solely on the lookin' purdy.
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,346
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by 480sparky View Post
    There are ways of complying, they just don't make those involved very happy. Don't want to drill a pop up into the stone counter? Pendant drop is code compliant, the woman of the house probably won't like it unless they have some sort of industrial design scheme.
  8. #8
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    19,581
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I don't understand the description. Can you post a photo?
    Until the photo arrives, here is my guess as to what you are trying to describe:
    • Stand to the left of the window, facing the wall.
    • Put your hand on the countertop, and slide it towards the wall until your finger touches the backsplash.
    • Keeping your hand on the countertop and your finger touching the backsplash, slide your hand to the right.
    • At some point, I imagine that your hand will still be touching countertop, but what is your finger touching?
      • Glass?
      • The bottom wooden vertical frame of the window?
      • The wooden horizontal surface of the bottom of the garden window, with the actual glass some distance further away from your hand?
    • As you continue sliding your hand to the right, your finger eventually touches the backsplash of the counter space to the right of the window.
    Can you use this description to clarify your situation?
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  9. #9
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    19,581
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    OK. Here is one possible approach. What do you all think?
    210.52(A)(2) clarifies what is meant by "wall space." But it starts by saying, "As used in this section. . . ." Since (A)(2) is part of (A), I infer that that clarification only applies within (A). Specifically, it does not apply to 210.52(C). In other words, we don't have a clarification of what is meant by "wall space," in the context of "countertop wall space." Therefore, we cannot begin by saying a floor-to-ceiling window in the family room counts as wall space, and conclude therefrom that a countertop-to-ceiling window in the kitchen also counts as wall space.
    I am inclined to go with Tim's post #2. It's not "countertop wall space" because there is no wall, and because we don't have a rule that says a window behind a kitchen countertop counts as wall space.
  10. #10
    Join Date
    Jul 2007
    Iowegia
    Posts
    18,538
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by charlie b View Post
    ..... It's not "countertop wall space" because there is no wall, and because we don't have a rule that says a window behind a kitchen countertop counts as wall space.
    Unless the local AHJ says it's a wall.
Posting Permissions
  • You may not post replies
  • You may not edit your posts
