    Quote Originally Posted by ceb58 View Post
    I agree as long as you follow the "closest point of entry" when the conduit emerges from the concrete no disco. As far as the other I would set a disconnect for the future feeder that way you don't have to mess with the POCO to get back into the meter base.
    In our jurisdiction, that would create a problem. If you set ONE disconnect at the meter for future use and feed from the meter underslab to your house service panel, we consider that a violation of 230.72
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  2. #12
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,360
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    In our jurisdiction, that would create a problem. If you set ONE disconnect at the meter for future use and feed from the meter underslab to your house service panel, we consider that a violation of 230.72
    If on same structure yes.

    Sounds like if it is a PITA to get POCO out to do such things best thing may be to install meter-main with dual main breakers, then you don't need POCO intervention to add something to the second main later on.