    320 Meter Socket, Service set up

    Hey everyone, I have a question regarding the service set up of a 320 meter socket.
    The set up is as follows...

    Have riser coming to the 320 meter. From the meter I have conduit run under the slab to a 200 amp main breaker house panel. Does this service need to have a disconnect on it by the meter socket?


    The plan is to have another dwelling unit in the future use the remaining Lugs in the 320 meter. Do I need a disconnect for the future service.

    Would love any input or suggestions on what to do differently!

  2. #2
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,609
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    In the jurisdictions that I am familiar with the install would be approved without any overcurrent at the meter.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  3. #3
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,270
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    In the jurisdictions that I am familiar with the install would be approved without any overcurrent at the meter.
    Same here, and with that in mind, 3 wire to each, as long as there is no metallic interconnection otherwise.
    Tom
    TBLO

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,346
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Someone long time ago mentioned on this site that a meter is just wide point in the service conductors (most typical installations where the meter is simply the POCO's cash register ahead of service disconnecting means) and gets no special treatment from NEC. You do about same thing with it as you would a junction or pull box in the service conductors.
    I live for today, I'm just a day behind.

  5. #5
    Join Date
    Jan 2014
    Location
    chicago, il, USA
    Posts
    451
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    How far from the meter socket to the main panel is it? I can't remember what the exact distance, I think its either 5 or 6 ft but if it exceeds that in some jurisdictions they require a disconnect at the meter.
    The world is round, you will get there no matter what path you take.

  6. #6
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,767
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    The only issue I see, is with this potential future dwelling unit, and whether that meter can serve both without disconnects. Take a look at 230.40.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  7. #7
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    1,175
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rlundsrud View Post
    How far from the meter socket to the main panel is it? I can't remember what the exact distance, I think its either 5 or 6 ft but if it exceeds that in some jurisdictions they require a disconnect at the meter.
    That’s usually from the point of entry. Most jurisdictions don’t consider “under the slab” as entering the structure, only the portion that is exposed coming out of the slab.

  8. #8
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,767
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mopowr steve View Post
    That’s usually from the point of entry. Most jurisdictions don’t consider “under the slab” as entering the structure, only the portion that is exposed coming out of the slab.
    And the NEC specifically says under 2" of concrete is considered outside.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  9. #9
    Join Date
    Jan 2008
    Location
    Raeford, NC
    Posts
    3,705
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree as long as you follow the "closest point of entry" when the conduit emerges from the concrete no disco. As far as the other I would set a disconnect for the future feeder that way you don't have to mess with the POCO to get back into the meter base.
    Organized people are people that are just too lazy to look for their stuff

  10. #10
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,938
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by WA Sparky View Post
    Hey everyone, I have a question regarding the service set up of a 320 meter socket.
    The set up is as follows...

    Have riser coming to the 320 meter. From the meter I have conduit run under the slab to a 200 amp main breaker house panel. Does this service need to have a disconnect on it by the meter socket?


    The plan is to have another dwelling unit in the future use the remaining Lugs in the 320 meter. Do I need a disconnect for the future service.

    Would love any input or suggestions on what to do differently!
    As others have said, this is fine by the NEC. However, it may not be OK with the POCO. Many POCOs have requirements as to where the service disconnect is in relation to the metering point.