User Tag List
Results 1 to 4 of 4
Thread: Swing Plug for Buss
  1. #1
    Join Date
    Jan 2016
    Melrose Park, IL USA
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Swing Plug for Buss
    Are the old style swing plugs legal to use for new construction?
    John Huffman
  2. #2
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,322
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    What's a swing plug?
    Welcome to the Forum.
    Rob
  3. #3
    Join Date
    Jan 2016
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by 29jennifer View Post
    John Huffman
    The kind of plug I'm referring to are the ones that the power is connected and disconnected to the line side of the branch circuit by the opening and closing of the door.
  4. #4
    Join Date
    Jan 2018
    SE Michigan
    Posts
    151
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Swing Jack Bulldog Bus Plug
    Swing jack, bus plugs are not compliant for new installs, because they are not capable of being operated from the floor. An older plant that still has these types, can continue to use them, on their old circuits.
    368.17 (C) Feeder or Branch Circuits. Where a busway is used as a feeder, devices or plug-in connections for tapping off feeder or branch circuits from the busway shall contain the overcurrent devices required for the protection of the feeder or branch circuits. The plug-in device shall consist of an externally operable circuit breaker or an externally operable fusible switch. Where such devices are mounted out of reach and contain disconnecting means, suitable means such as ropes, chains, or sticks shall be provided for operating the disconnecting means from the floor.