    Quote Originally Posted by electrofelon View Post
    Were they old or relatively new?
    Old ones but I have seen some not function right out of the box.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  2. #12
    Join Date
    Jun 2003
    Posts
    11,263
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by pjones View Post
    Sorry, I’m having a hard time figuring this one out. What’s an FOP test?
    You need a fairly good meter with a mili volt range. Multipole breakers with the same load should have approximately the same VD across the Line 1 to Load 1, etc. 100mv or less.
    Zero volt drop would mean zero load to me.
    Tom
    TBLO
  3. #13
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,338
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Anything that creates undesired heat within is going to increase the possibility of tripping on thermal, can even be heat that originates at a termination or bus connection and is conducted to interior of the unit.
    I live for today, I'm just a day behind.
  4. #14
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,764
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    I could see that, but what isn't clear to me is how the mag function would go bad to make it trip early.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  5. #15
    Join Date
    Jun 2004
    Posts
    5,764
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    I guess I am lucky. Can't ever remember getting a bad breaker out of the box, other than maybe one or two that wouldn't latch closed. Can't ever remember one being overly sensitive.
  6. #16
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,338
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I see mechanical wear being a bigger issue that may affect mag function, could make it trip easier or could make it need higher mag field to make it trip, depends on what/how an item wears out.
  7. #17
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,313
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    That would more likely be from mechanical wear from being used daily as a switch rather than just age.
  8. #18
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,338
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    And could make it trip at higher or lower fault current depending on wear conditions I would think, or at very least affect clearing time compared to when it was new.
  9. #19
    Join Date
    Jul 2013
    Moab, UT USA
    Posts
    298
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Too Many....
    Quote Originally Posted by LarryFine View Post
    FOP = Fall Of Potential
    It means measuring the voltage between the line and load terminal of one pole at a time. You're looking for voltage drop where there shouldn't be any. In theory, there should be zero volts across a closed switch or breaker.
    I would check the line current with a clamp-on ammeter.
    There are TOO MANY, WAY TOO MANY ACRONYMS, and they are becoming bothersome for this reason. There are other aspects about them which make them even more distasteful that there is no need to go into. Some of the exact same ones cross over into completely different trades and mean different things.
    There needs to be as master list on the forum possibly.
    Microwave Radiation Dangers should be openly discussed
  10. #20
    Join Date
    Mar 2008
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    10,548
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by StarCat View Post
    Good point, especially since I would not use FOP to describe what I would call a voltage drop test across the terminals of the breaker.
    When I hear Fall of Potential used, I pretty much instantly think about grounding electrode resistance tests.