    Fixtures; Fixture, Switch and Receptacle Enclosures in Horse Barns

    Hello,

    In a horse barn would it meet code to install light switches and receptacles in 4 x 4 boxes in areas that are not prone to getting wet? Are fluorescent strip lights or wraparounds permitted? Article 547 is a little vague.

    Thanks,
    Ravenvalor
    Electrical Contractor
    Piedmont Region of NC

    "Good day and good premises." (Ayn Rand)

  2. #2
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2017
    Posts
    5,261
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Ravenvalor View Post
    Hello,

    In a horse barn would it meet code to install light switches and receptacles in 4 x 4 boxes in areas that are not prone to getting wet? Are fluorescent strip lights or wraparounds permitted? Article 547 is a little vague.

    Thanks,
    There is also dust to consider, along with wet/damp locations. A regular 4-square would not meet the requirements in either wet or dusty locations.
    Strip lights would also be a "no-no" in wet or dusty areas, also they wouldn't be guarded if in an area that requires them to be.
    You've also got to consider what might be reachable/accessible to the animals. Horses can be very destructive.
    If you aim at nothing, you will hit it every time!

  3. #3
    Join Date
    Oct 2007
    Location
    Piedmont region of NC
    Posts
    793
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Little Bill View Post
    There is also dust to consider, along with wet/damp locations. A regular 4-square would not meet the requirements in either wet or dusty locations.
    Strip lights would also be a "no-no" in wet or dusty areas, also they wouldn't be guarded if in an area that requires them to be.
    You've also got to consider what might be reachable/accessible to the animals. Horses can be very destructive.
    Yes sir they sure can be. Id hate to be the jockey in the front of a pack in a horse race when my horse falls.

    Thanks...
    Ravenvalor
    Electrical Contractor
    Piedmont Region of NC

    "Good day and good premises." (Ayn Rand)

  4. #4
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,234
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Little Bill View Post
    There is also dust to consider, along with wet/damp locations. A regular 4-square would not meet the requirements in either wet or dusty locations.
    Strip lights would also be a "no-no" in wet or dusty areas, also they wouldn't be guarded if in an area that requires them to be.
    You've also got to consider what might be reachable/accessible to the animals. Horses can be very destructive.
    At what level is an area considered "dusty"? One of the area inspectors posted a picture of dust on an enclosure, warning us of having the right enclosures. He didn't fill us in on how long it took to accumulate. As I told him, I've seen worse in homes.
    Tom
    TBLO

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,295
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    At what level is an area considered "dusty"? One of the area inspectors posted a picture of dust on an enclosure, warning us of having the right enclosures. He didn't fill us in on how long it took to accumulate. As I told him, I've seen worse in homes.
    Seen worse animal waste conditions in homes a few times compared to a horse barn as well.

    And I don't do racing horse facilities - those sometimes live in better conditions than "moderate" people do.
    I live for today, I'm just a day behind.

  6. #6
    Join Date
    Dec 2006
    Location
    Eastern Oregon
    Posts
    3,782
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We tend to use gasket vaporproof fixtures in the ag buildings we do, for two reasons. Dust.....and also, flies. Dead flies like to collect in light fixtures in ag buildings.

    In the dairies we wire, we use a combination of pvc, rigid, emt, mc, romex, pvc flex, sealtite, etc. It just depends on where we are in the building and what the situation calls for.

    The simplest is to call your inspector and feel him out.

  7. #7
    Join Date
    Oct 2007
    Location
    Piedmont region of NC
    Posts
    793
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Cow View Post
    We tend to use gasket vaporproof fixtures in the ag buildings we do, for two reasons. Dust.....and also, flies. Dead flies like to collect in light fixtures in ag buildings.

    In the dairies we wire, we use a combination of pvc, rigid, emt, mc, romex, pvc flex, sealtite, etc. It just depends on where we are in the building and what the situation calls for.

    The simplest is to call your inspector and feel him out.
    I believe that vaportight fixtures are a great idea in a horse barn. Our customer has 8' HO strip lights that may be 20 years old. We all know how a fluorescent light will throw an ember once in a while. Just yesterday at another job location there was a f32t8 fluorescent socket sparking and glowing.
    Ravenvalor
    Electrical Contractor
    Piedmont Region of NC

    "Good day and good premises." (Ayn Rand)

  8. #8
    Join Date
    Apr 2015
    Location
    phoenix az
    Posts
    313
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    even the WP fixtures dont stay clean very long in stables... or devices mounted at standard heights and subject to damage from barrows or utvs ect.. the other thing i learned? you are more likely to get bit by a horse than kicked.. now that hurts! sea biscuit was getting tired of me taking too long fixing the auto walker...