    I have a 4000a switchgear, and i have been working on one-line diagrams on MCC's that feeds off of switchgear, I have several 1200a breakers supplying MCC's. I want to know total continuous loads, how do I complete this..
    thanks...
  2. #2
    Join Date
    Mar 2014
    South Florida
    Posts
    363
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Michael.D View Post
    thanks...
    How did someone come up with the 1200 amp for the MCC? You do the same thing with the switchgear. Add up all continuous loads and add 25% of the largest continuous load.
  3. #3
    Join Date
    Oct 2007
    New Jersey
    Posts
    6,640
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    thanks...
    You can't back-calculate the continuous loads, you have to know what they are going in.
  4. #4
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,781
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Is this a new install, or existing?
    We use loggers quite a bit, if it's existing and we have time to do it.
  5. #5
    Join Date
    May 2019
    Ga
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    thanks, this was a wood pellet plant built around 2007, our company just aquired it Jan 2019, looking to upgrade. i did the same calculations as MCC's, numbers looked alittle high for me so i thought i would ask this forum..One question, you use 25% continuous load of the highest MCC load? this is how I figured it..
  6. #6
    Join Date
    Mar 2014
    South Florida
    Posts
    363
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    you can do it a couple ways.
    first is you can put a power meter on it for 30 days that logs demand every 15 minutes. take the max value from that data set and multiply it by 125%. that is your minimum feeder size. add to it any new loads if you need to install new equipment.
    second.. say your MCC has 5 x 25 hp pumps that operate continuously. you also have a 100 hp fan that operates continuously. assuming a 460V system, your 25 hp pumps each draw 34 amps (according to the NEC). the fan draws 124 amps. add up all continuous loads to determine connected load: 5 x 34 + 124 = 294 amps. last we have to add 25% of the largest continuous load: 124 * 0.25 = 31 amps for determinig the minimum feeder size.. which would be 294 + 31 = 325 amps.
    repeat this process for each MCC and add up all of their connected loads. then determine the largest motor connected to any one of the MCC's and add 25% of that to determine the minimum feeder size for the switchgear. for example, if you had 5 MCC's, all identical to the example above, the connected load for the switchgear would be 294 x 5 = 1470 amps. last we add 25% of the largest motor (100 hp fan): 1470 + 124 x 0.25 = 1504 amps minimum feeder size.
  7. #7
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,742
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    thanks...
    What are you trying to accomplish exactly? If you want to determine existing loads to find extra capacity, then you need a power logger. I don't really see the point in doing an NEC calculation on an existing system, all it will do is over estimate your usage by a factor of 2 to 2.5.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  8. #8
    Join Date
    Mar 2014
    South Florida
    Posts
    363
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    we regularly run into this exact issue because we use NEC calculations to make additions. there is not always time or money to place a logger. NEC calc's always over estimate the load, and rightly so. we make what adjustments we can based on anticipated operation, but there is no way to anticipate the diversity factor without logging the demand over a long period. the only short coming to this method (logging) is you must take into consideration the annual operation of the plant. a waste water plant in florida will have higher peak flows during the travel season. whereas a wood pellet facility demand will go up and down based on how many units the plant must produce.
    if the switchgear is the service entrance point for the plant, consider contacting the utility authority and requesting demand data for the last 12 months. they should be able to tell you what the peak demand was during that time period.