    Wire Size Min Cir ampacity

    I have a project where the a HVAC compressor replacement unit for a building came in different than on the plans and what is existing. I have to tell the bad news. I am looking to see if I am correct first.

    The wiring is 500MCM THW ( short distance 15' from the MSB so not a real big deal )
    The conduit is inside.

    The nameplate is MCA 405a 208 3 phase
    MOCP 600a
    So THW is rated at 70 deg C only 380a ( does not have a 90 deg rating)

    Since it is less than the required MCA of 405a the wire must be up sized.
    I don't think there is a next higher rule for MCA-
    Am I correct?

  2. #2
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,936
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree. You do not have enough ampacity. The next size up does not apply here.

  3. #3
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,730
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yep, MCA means MINIMUM Circuit Ampacity, not "More-or-less" Circuit Ampacity...
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  4. #4
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,875
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks , so many have this confused and I wanted to be sure.

    So next question.
    I was thinking parallel 4/0 as the conduit is a full boat with 600 mcm and I really don't want to pull that.
    Do I need the 4/0 or can I go with 3/0 and the 90 deg column. I don't think the terminals are rated and I don't think there is room to splice a stub of wire.

  5. #5
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,936
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sierrasparky View Post
    Thanks , so many have this confused and I wanted to be sure.

    So next question.
    I was thinking parallel 4/0 as the conduit is a full boat with 600 mcm and I really don't want to pull that.
    Do I need the 4/0 or can I go with 3/0 and the 90 deg column. I don't think the terminals are rated and I don't think there is room to splice a stub of wire.
    The math says if you put this all in 1 raceway you will need 4/0 90 degree conductor. This would give you an adjusted ampacity of 416 that would be acceptable for 75 degree terminals.

  6. #6
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,936
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What size raceway do you have?

  7. #7
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,875
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    3" PVC I believe

  8. #8
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,936
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sierrasparky View Post
    3" PVC I believe
    6, 4/0 THHN plus an EGC would fit in this OK.

  9. #9
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,875
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks to you all.

    One more question of course.

    So when using the 90deg column you use for wires inside conduit. When are you allowed to remove the derating in ampacity for conductor heating, more than 3 conductors in conduit?

    How much length must there be past the neck of the conduit to be considered no longer heating and then use the 70 deg column with no derating?

    Thanks

  10. #10
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,289
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sierrasparky View Post
    Thanks to you all.

    One more question of course.

    So when using the 90deg column you use for wires inside conduit. When are you allowed to remove the derating in ampacity for conductor heating, more than 3 conductors in conduit?

    How much length must there be past the neck of the conduit to be considered no longer heating and then use the 70 deg column with no derating?

    Thanks
    If you are no longer in raceway/cable then the adjustment no longer applies.

    Aux gutters/wireways - I think if longer than 30 feet you must apply the adjustment.
    I live for today, I'm just a day behind.