    Quote Originally Posted by myspark View Post
    You are joking .
    This not how we run business. This working relationship is ok if you are a regular customer of Bob's Butcher shop.
    I don't want my better judgment become clouded just because of my relationship with supplier.
    I wasn’t. It’s your choice. My opinion.
    Tom
    TBLO
  2. #22
    Join Date
    Jun 2006
    NoDak
    Posts
    449
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    RTFM
    I am doing...
    Regarding control wiring,
    0.3mm^ - 0.75mm^ , according to Google equates to ~ 18awg - 22awg...?
    What do most of you use for your control wire within the drive enclosure?
    I'm assuming you'd be using 600v rated wire...
  3. #23
    Join Date
    Jan 2019
    UK
    Posts
    457
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by sw_ross View Post
    I am doing...
    Usually we used 1mm^2. Some customers specified 1.5mm^2 for control wiring. That would be 17 AWG and 16 AWG. If could get these.
    The difference in cost would normally be insignificant but then we mostly supplied fairly large VFDs.
  4. #24
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,277
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I am doing...
    Often control wiring can be class 2 circuit.
  5. #25
    Join Date
    Jun 2006
    NoDak
    Posts
    449
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    control wiring question
    Given this information in the manual;
    1) If i wanted to jog the motor either forward or reverse, I would wire up 2 pushbuttons (non-latching), using SD as common and STF for forward and STR for reverse? (no voltage input allowed)
    2) If i wanted to use a pot. to control motor speed, I would use terminals 1, 2, & 3? Does the drive supply the 0-10v?
    Thanks for helping!
  6. #26
    Join Date
    Jun 2003
    Posts
    11,224
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for helping!
    That would work, but usually there is another input you can assign to JOG with a preset speed.
    Yes, Yes.
    Tom
    TBLO
  7. #27
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,277
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    Yes, Yes.
    Terminals can be reprogrammed for other functions according to one of the notes, what is printed there is the default settings.
  8. #28
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,277
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    1) If i wanted to jog the motor either forward or reverse, I would wire up 2 pushbuttons (non-latching), using SD as common and STF for forward and STR for reverse? (no voltage input allowed)"No voltage input allowed" means do not use an external voltage source, voltage for this circuit is supplied by the drive, but yes if you don't change any the functions from default, any signal on those two terminals will run the motor at whatever speed is selected. Many times drives have FWD and REV inputs as well as a "Run" or other "enable" input. On those you would need a direction input as well as a run input before the drive will be active.
    Thanks for helping!
    Actually the terminals on the drive should be labeled 10, 2 and 5, 0-10V is another control scheme and is between terminals 2 and 4 when used along with 4-20mA being a possible control scheme. Some of these functions also may be changeable in the parameter settings, but what is printed there is likely the default settings.
    Control voltage for the speed pot comes from the drive though, all you need to do is connect it to those terminals.
  9. #29
    Join Date
    Jun 2006
    NoDak
    Posts
    449
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks
  10. #30
    Join Date
    Jun 2003
    Posts
    11,224
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yup, 10,2,5
    Tom
    TBLO
Posting Permissions
  • You may not post replies
  • You may not edit your posts