    Electrical Disconnect for motor operated appliance

    2014 NEC article 422.31 (C) requires a disconnect for motor operated appliances greater than 1/8HP.
    It requires the disconnect to be within site of the motor (IE the panel or an additional disconnect)
    It does not mention if the additional disconnect has to be readily accessible.
    Can anyone point me in the right direction if the additional disconnect (not the panel) is required to be readily accessible? Does 430.107 apply? and could the panel be considered the accessible disconnect?

    I am aware of the 2017 code changes however this was designed using the 2014 cycle.
    Thanks.

  2. #2
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,314
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If the disconnect is or contains an overcurrent device, see 240.24. subpart (4) may allow access by portable means.

    Others switches see 404.8(A) and exceptions.
    I live for today, I'm just a day behind.

  3. #3
    Join Date
    May 2015
    Location
    Massachusetts
    Posts
    16
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks Kwired