    Need to have some type of hood over a range. If gas it needs to exhausted to the outside. Not a NEC thing but a Building code thing.
    Why would one install a range and no hood or downdraft

    Again if it is built in it needs a dedicated circuit. If on a shelf free standing then no.

  2. #12
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,736
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    OP has no idea what he is talking about.

    -Hal

  3. #13
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,876
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hbiss View Post
    OP has no idea what he is talking about.

    -Hal
    Easy now.

  4. #14
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,385
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Range hood/micro combo are typically cord and plug connected and therefore require an individual branch circuit.

    (4) Range Hoods. Range hoods shall be permitted to be
    cord-and-plug-connected with a flexible cord identified as
    suitable for use on range hoods in the installation instruc-
    tions of the appliance manufacturer, where all of the fol-
    lowing conditions are met:
    (1) The flexible cord is terminated with a grounding-type
    attachment plug.
    Exception: A listed range hood distinctly marked to iden-
    tify it as protected by a system of double insulation, or its
    equivalent, shall not be required to be terminated with a
    grounding-type attachment plug.
    (2) The length of the cord is not less than 450 mm (18 in.)
    and not over 900 mm (36 in.).
    (3) Receptacles are located to avoid physical damage to the
    flexible cord.
    (4) The receptacle is accessible.
    (5) The receptacle is supplied by an individual branch
    circuit.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #15
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,876
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Range hood/micro combo are typically cord and plug connected and therefore require an individual branch circuit.
    Yes , several code sections point to the same requirement.
    Individual branch circuit.

    OP has not been back, I bet he gets it.

  6. #16
    Join Date
    Feb 2003
    Location
    San Jose, CA
    Posts
    1,569
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I still have no idea what the OP is calling a microwave. They stated its not an oven and its not a hood.