    Service drop conductor clearences from final grade

    For a residential backyard only subject to foot traffic the Nec states 10' clearences of conductors yet the power company states 12' in their requirements. Is this a case where the power company trumps the nec in this instance/jurisdiction? Attached is a screen shot of power companies requirement. Any input would be appreciated. I would assume that my weatherhead/drip loop would have to be at 12' based on power companies paperwork.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Screenshot_2019-05-22-20-23-11.jpg 
Views:	35 
Size:	10.5 KB 
ID:	22977   Click image for larger version. 

Name:	Screenshot_2019-05-22-20-19-17.jpg 
Views:	35 
Size:	9.8 KB 
ID:	22978  

  2. #2
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    4,729
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    POCO trumps the NEC.

    -Hal

  3. #3
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,260
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    POCO wins as being more restrictive. Our SED would not allow an installation less restrictive than the NEC.
    Tom
    TBLO

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,376
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    In most cases the service drop condcutors are outside of the purview of the NEC.

    90.2(B)Not Covered.
    This Code does not cover the following:
    (5) Installations under the exclusive control of an electricutility where such installations
    a. Consist of service drops or service laterals, and associated metering, or
    b. Are on property owned or leased by the electricutility for the purpose of communications, metering,generation, control, transformation, transmission, ordistribution of electric energy, or
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    Apr 2019
    Location
    Arvada, Co
    Posts
    10
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    In most cases the service drop condcutors are outside of the purview of the NEC.
    Would that apply to weatherhead height also then I assume?

  6. #6
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,878
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Most POCO's require not less than a 12' sag in the triplex from the pole to the house. However, there are many instances where houses are located fairly close to one another (i.e. cities and small townships) and where houses are close to the street. Where a utility pole is on the same side of the street and close to the house (let's say 20' or less) and where the triplex runs up to that particular house the POCO will allow the point of attachment on the house to be at 10'. BUT, I would contact the POCO rep. and make sure it's OK before you go ahead and do that.

  7. #7
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,260
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Qwertytfc View Post
    Would that apply to weatherhead height also then I assume?
    No, 230.24(B) is 10'. That would be the low point of the drip loop before entering the weather head. The WH would be above that.

    eta: POCO requirement of 12' would put you above that point.
    Tom
    TBLO

  8. #8
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,376
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    In most cases the service drop conductors are outside of the purview of the NEC.
    Quote Originally Posted by Qwertytfc View Post
    Would that apply to weatherhead height also then I assume?
    You would have to determine where the service point is, on an overhead service this is usually where the POCO service drop connects to the SEC's so the weatherhead is governed by the NEC rules.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted