    Quote Originally Posted by growler View Post
    I have put 3 #6 and 1 #10 in 1" elbow with no problems.

    Naturally they will be stranded but the insulation type makes all the difference. THHN is about the easiest to pull.
    You had no problems because a 1" elbow allows #6. But don't try that in a 3/4" elbow. Did that once by accident and was glad the inspector didn't notice. Wires got pretty scuffed in the process but it tested okay and didn't fault. Looked at the elbow markings afterward and realized why I had such a tough time.

    Moral of the story is that when using these things you've got to watch out because conduit fill tables will tell you that you can run a 3-wire circuit plus ground with a wire size larger than the pulling elbow allows for that size raceway. Doesn't happen with normal LB fittings so far as I've noticed.

  2. #12
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,359
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    You had no problems because a 1" elbow allows #6. But don't try that in a 3/4" elbow. Did that once by accident and was glad the inspector didn't notice. Wires got pretty scuffed in the process but it tested okay and didn't fault. Looked at the elbow markings afterward and realized why I had such a tough time.

    Moral of the story is that when using these things you've got to watch out because conduit fill tables will tell you that you can run a 3-wire circuit plus ground with a wire size larger than the pulling elbow allows for that size raceway. Doesn't happen with normal LB fittings so far as I've noticed.
    Are short bodies like pictured even available larger than 3/4? I never seen one.

    Also never seen any wire size information on a short body fitting.
    I live for today, I'm just a day behind.

  3. #13
    Join Date
    Jun 2003
    Location
    NE (9.06 miles @5.9 Degrees from Winged Horses)
    Posts
    11,272
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    Are short bodies like pictured even available larger than 3/4? I never seen one.

    Also never seen any wire size information on a short body fitting.
    I haven't either, but I haven't looked either.
    Tom
    TBLO

  4. #14
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    738
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    Are short bodies like pictured even available larger than 3/4? I never seen one.

    Also never seen any wire size information on a short body fitting.
    I've seen the ones with a removable cover in 1" at the box store.

  5. #15
    Join Date
    May 2019
    Location
    Davis, CA Yolo County
    Posts
    21
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Reply

    Well - I was asking the question after the install. And yes, the wires got a little scuffed. That is three #6 and a #8 in 3/4 (not 1"). Conduit fill for the straight run is OK. The Elbows are not labeled and it is tight. Will it pass? Who knows.

    Also - a related question: Some elbows have no threads, only set screws. Others have threads and set screws. Can one use the threaded with set screws directly with the EMT, or does one have to use (two) connectors (with set screws, one for each end)?

  6. #16
    Join Date
    May 2019
    Location
    Davis, CA Yolo County
    Posts
    21
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Additional detail

    Both elbows are near the very ends of the run. I could replace them easily. Thoughts on doing that? Why - why not?

  7. #17
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,753
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Pulling elbows are available for 2" from Gordon Electric

    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  8. #18
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,534
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ESolar View Post
    Also - a related question: Some elbows have no threads, only set screws. Others have threads and set screws. Can one use the threaded with set screws directly with the EMT, or does one have to use (two) connectors (with set screws, one for each end)?
    The ones with set-screws can be used without connectors.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA