Thread: Transformer Primary Conductors Calculation

  1. #1
    Join Date
    Dec 2018
    Location
    New York, NY, USA
    Posts
    54
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Transformer Primary Conductors Calculation

    Hey Guys,

    We have a Solar system installed with the following specs:
    - Voltage: 480 V
    - Current: 1080 A

    This is fed into the secondary of the 1000 kVA transformer with 4kV on the primary whose spec. is:
    kVA= (1.732 x 480 x 1080)/1000 = 897.895 kVA (1000 kVA is used)

    From this the primary current will be:
    I = 897.995*1000/1.732*4000 = 129.6 A

    The POCO asked us to use a 2/0 wire for the primary, but I wanted to verify this so, Can someone please provide a step by step process to calculate the conductor size for the primary according to NEC?

    Thanks in Advance

  2. #2
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,770
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Are you taking service at primary voltage? Where does does the 4kv go? Where is the service disconnect? Those answers will help.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  3. #3
    Join Date
    Dec 2018
    Location
    New York, NY, USA
    Posts
    54
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Are you taking service at primary voltage? Where does does the 4kv go? Where is the service disconnect? Those answers will help.
    The 4kV is directly connected to the grid which is the service voltage from the POCO, this is an underground run. Hope this helps. Please check attached
    Name:  1.jpg
Views: 372
Size:  17.4 KB
    Last edited by TheElectrician; 05-23-19 at 02:52 PM.

  4. #4
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,770
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Where is the service disconnect?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  5. #5
    Join Date
    Dec 2018
    Location
    New York, NY, USA
    Posts
    54
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Where is the service disconnect?
    Do you mean the primary protection of the transformer? if so it is not added in this one line, but there is a disconnect before (on the secondary side) of the transformer.
    Last edited by TheElectrician; 05-23-19 at 05:28 PM.

  6. #6
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    738
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Did you ask the PoCo rep why they are requiring this size conductor?

    What size conductor do you want to install, and what table would you use for its ampacity rating?
    Last edited by oldsparky52; 05-24-19 at 07:04 AM.

  7. #7
    Join Date
    Feb 2013
    Location
    India
    Posts
    2,713
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by TheElectrician View Post

    The POCO asked us to use a 2/0 wire for the primary,

    Thanks in Advance
    Once you provide it, it becomes their property and they would maintain it as the 1000 KVA transformer is theirs and so not covered by NEC. Isn't it?

  8. #8
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,916
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sahib View Post
    Once you provide it, it becomes their property and they would maintain it as the 1000 KVA transformer is theirs and so not covered by NEC. Isn't it?
    My thought too.
    Perhaps not the owning but the specifying as to being a feeder into primary power.

  9. #9
    Join Date
    Dec 2018
    Location
    New York, NY, USA
    Posts
    54
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by oldsparky52 View Post
    Did you ask the PoCo rep why they are requiring this size conductor?

    What size conductor do you want to install, and what table would you use for its ampacity rating?
    Yes, I asked the power company, they just asked me to follow their spec sheet and didnt give any further information on how they came up with it. They just are not giving that information. I was using the the teriplex conductor table 310.60(74) AL for 15kV, for sizing it using the derate factor 1.25

  10. #10
    Join Date
    Dec 2018
    Location
    New York, NY, USA
    Posts
    54
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sahib View Post
    Once you provide it, it becomes their property and they would maintain it as the 1000 KVA transformer is theirs and so not covered by NEC. Isn't it?
    You are right, although they provided the t/f the customer owns it, but still they wanted to install the conductor by their specs, and I wanted to figure out how they came up with that number.