630.12 and 630.13

Status
Not open for further replies.

Dale001289

Senior Member
Location
Georgia
As has been noted, it doesn't say "receptacle" it says "each arc welder." For the case of one circuit feeding multiple welders or multiple welder receptacles, I am not sure I agree that the ocpd can't be the disconnect for all welders/receptacles.


Look at it logically. Would you feel comfortable with six welders striking at the same time, each rated at 40A, and ONE overcurrent device protecting the cable at 60A?
See T630.11(A) for duty cycle demand factors.
 