    Does anyone know the exact code for the requirement?

  2. #2
    Join Date
    Feb 2013
    Location
    India
    Posts
    2,713
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    For (outdoor) diesel tank, code is there for placement of fire extinguisher. For diesel generator, it is simply stated to keep near fire extinguisher in one installation manual.

  3. #3
    Join Date
    Sep 2003
    Location
    Connecticut
    Posts
    257
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    OSHA, 29 CFR 1910.157 "1910.157(d)(4) "The employer shall distribute portable fire extinguishers for use by employees on Class B fires so that the travel distance from the Class B hazard area to any extinguisher is 50 feet (15.2 m) or less."

    A 10-lb. dry chemical extinguisher rated 2A:10B:C ought to be sufficient.