User Tag List
Results 1 to 9 of 9
Thread: Disconnect on Exterior
  1. #1
    Join Date
    Jun 2013
    loveland colorado
    Posts
    84
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I cant seem to find the answer to this in the code book...
    If the meter main is on a pole and the house sits 100' away do you need a service disconnect on the outside of the house or can you LB into the house and have the next disconnect in the breaker panel?
    I believe the rule is, if its over 50' or not in sight of then you need a main on the exterior. Could someone please help and tell me if I am correct in what I am thinking?
  2. #2
    Join Date
    May 2014
    Marlborough, Massachusetts USA
    Posts
    400
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I apologise, no code reference. I mount electrical meters on remote pedestals often hundreds of feet away and never worried about a separate disconnect. Maybe you would need a separate disconnect if your panel is not adjacent to the point of the service entrance.
  3. #3
    Join Date
    Dec 2011
    Wisconsin
    Posts
    670
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    225.32 Disconnect needed outside or inside nearest the point of entrance of the conductors.
  4. #4
    Join Date
    Mar 2003
    Vermont
    Posts
    2,525
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    but isn't 225 for outside branches & feeders? ~RJ~
  5. #5
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,939
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    This is an outside feeder as the OP said he has a meter/Main remote from the house. A disconnect is required at the house. He also needs both an EGC and neutral conductor for this feeder.
  6. #6
    Join Date
    May 2014
    Posts
    400
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I need to pay better attention. I missed the main part on the first post.
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,359
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    225 and 230 have basically same requirement. The issue with this case is whether the disconnect at the pole is considered service disconnect or not. NEC pretty much says it is, however some jurisdictions do say if that disconnect is utility supplied that they do not consider it to be the serivce disconnect. About all that changes is the need for an EGC to be run to the house, a disconnect is still needed at house either way.
    I live for today, I'm just a day behind.
  8. #8
    Join Date
    Dec 2018
    Boston
    Posts
    8
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Check out here also might help you
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,359
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Stephbaker View Post
    That thread is primarily about how far can conductors enter the building before a disconnect is needed, OP here is asking if the disconnect can be on a pole (50 feet in his case) away from the structure.