    Physical protection behind crown molding

    Running romex where the wall and ceiling meets. Going to be hidden by crown moulding.. 300.4 only mentions notches in wood or boring through studs.... would I need to use a different raceway behind the crown molding?
    .....Still just happy to be here.....

  2. #2
    Join Date
    Feb 2003
    Location
    Pennsylvania
    Posts
    2,756
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shputnik View Post
    Running romex where the wall and ceiling meets. Going to be hidden by crown moulding.. 300.4 only mentions notches in wood or boring through studs.... would I need to use a different raceway behind the crown molding?
    (F) Cables and Raceways Installed in Shallow Grooves.

    You need 1&1/4 free space or some type of protection for the cable

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,389
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shputnik View Post
    Running romex where the wall and ceiling meets. Going to be hidden by crown moulding.. 300.4 only mentions notches in wood or boring through studs.... would I need to use a different raceway behind the crown molding?
    I see no NEC wording that would prohibit this without cable protection.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted