    I just noticed a proposed TIA for 210.52. I thought this may be of interest to all.. Please comment
    210.52(C)(2) Island and Peninsular Countertops and Work SPurfaces. Receptacle outlets
    shall be installed in accordance with 210.52(C)(2)(a) and (C)(2)(b).
    (a) At least one receptacle shall be provided for the first 0.84 m2 (9 ft2), or fraction thereof, of
    the countertop or work surface. A receptacle outlet shall be provided for every additional
    1.7 m2 (18 ft2), or fraction thereof, of the countertop or work surface.
    (b) At least one receptacle outlet shall be located within 600 mm (2 ft) of the outer end of a
    peninsular countertop or work surface. Additional required receptacle outlets shall be
    permitted to be located as determined by the installer, designer, or building owner. The
    location of the receptacle outlets shall be in accordance with 210.52(C)(3).
    A peninsular countertop shall be measured from the connected perpendicular wall.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  2. #2
    Join Date
    Apr 2003
    Fort Collins, Colorado
    Posts
    1,763
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    My opinion
    Throw out (a)
    Keep only the first sentence, the reference to 210.52(C)(3) & the last sentence of (b)
    P. S it's late in the day & I'm smelling beer.
    Ron
  3. #3
    Join Date
    Dec 2011
    Wisconsin
    Posts
    681
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    According to the substantiation, the only thing they did was add the last sentence. It was apparently omitted by mistake in the first two drafts. The rest of it was that way through the whole process.
  4. #4
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,872
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by packersparky View Post
    That is correct but I had missed the first drafts on this
  5. #5
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,531
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Do you have the prior wording for comparison?
    Rob
    All responses based on the 2014 NEC unless otherwise noted
  6. #6
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,872
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    The original proposal was the same as above without the last sentence and obviously the previous wording to that is in the nec 2017
    Not sure if that answers your question