Thread: PV feeder voltage drop - California

  1. #1
    Join Date
    May 2019
    Location
    Santa Rosa, Ca. Sonoma County
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    PV feeder voltage drop - California

    California electrical code requires that voltage drop does not exceed 5% total. This allows for 2% on feeders and 3% on branch circuits. I have seen countless PV systems designed with up to 5% drop. I'm guessing this is allowed because there are no branch circuit loads? Or have these systems all been in violation of the California regulations?
    TIA!

  2. #2
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    790
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The AC drop on PV systems is usually limited to around 2% so the inverter does not trip off on overvoltage. Sometimes PV designers list a total voltage drop number that sums the AC and DC voltage drops, why I don't know, and that can get over 5%. If you are seeing AC voltage drops of 5% then that's just poor design. They might have some really irritating intermittent inverter shutdowns.

  3. #3
    Join Date
    May 2011
    Posts
    5,463
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    That's the California Energy Code, not electrical code. It does not apply to residential installations. It is arguable that with no 'loads' involved, it does not apply to PV circuits. DC side voltage drop doesn't count (not a feeder or branch circuit). I too am a bit skeptical that you've seen 'countless' PV systems with 5% AC side voltage drop.

  4. #4
    Join Date
    May 2014
    Location
    california
    Posts
    165
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I’d have to do the math but it’s a pretty short run from the inverter to the panel (most systems) not real difficult to size the conductors for 1% on a typical residential <10kva system.

    I could be wrong though.

  5. #5
    Join Date
    May 2019
    Location
    Santa Rosa, Ca. Sonoma County
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Well, here's the scenario: We're backfeeding 300A from 147kW commercial ground mount. The feeder length is a little over 1000' and it was designed with 350mcm. This is 480V 3-phase.

    When I say I've seen countless systems designed with up to 5% voltage drop, I mean that I worked with a team of designers/engineers that used 5% as a maximum on their designs but that doesn't mean that figure was actually routinely reached. Also, that could have been factoring in DC drop as well, I'm not sure.

    I'm an operations manager, not a designer or engineer. I'm following the design provided by an engineer but it was brought to my attention that the voltage drop might be too high on this 1000+ foot run because CA regs dictate no more than 2%. The inverters themselves won't start tripping until about 5% drop is reached and I believe this puts us somewhere around 3%. I'm more just concerned about compliance with regulations. Thoughts?

  6. #6
    Join Date
    Sep 2012
    Location
    Clinton, WA
    Posts
    104
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    147 kW at 480V 3Ph = 177A line current. Are you sure your 300A figure is correct? My VD calculator is telling me that the VD for a 1000' 480V 3Ph 3W circuit with 300A through a #350 AL conductor is 6.56%. This would push the voltage up to 511V at the inverter if grid voltage is nominal. This shouldn't cause the inverter to shut down, but it seams a bit high. There may be additional VD between the feeder and transformer as well. If I change the current value to 177A, the voltage drop is 3.87%, which results in an inverter voltage of 499V.

  7. #7
    Join Date
    May 2019
    Location
    Santa Rosa, Ca. Sonoma County
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by PWDickerson View Post
    147 kW at 480V 3Ph = 177A line current. Are you sure your 300A figure is correct? My VD calculator is telling me that the VD for a 1000' 480V 3Ph 3W circuit with 300A through a #350 AL conductor is 6.56%. This would push the voltage up to 511V at the inverter if grid voltage is nominal. This shouldn't cause the inverter to shut down, but it seams a bit high. There may be additional VD between the feeder and transformer as well. If I change the current value to 177A, the voltage drop is 3.87%, which results in an inverter voltage of 499V.
    Your 177A figure is probably accurate in terms of actual production but we're using two SE100k SolarEdge inverters that have a max output rating of 120A each. Multiplied by 1.25 that puts it at 150A each.

    https://www.solaredge.com/sites/defa...tasheet_na.pdf

    The spec sheet shows "AC Output Voltage Minimum-Nominal-Maximum(1) (L-L) 422.5 - 480 - 529 Vac". So it looks like even the worst case scenario as far as VD will still keep the voltage within the manufacturers parameters. Not ideal but doable, yeah?

  8. #8
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    790
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Section 130.5 of the 2019 CA Energy Standard covers electrical distribution system voltage drop. Source to load the combined voltage drop through feeders and branch circuits has to be 5% or less, not 2% on feeders and 3% on branch. This is not a requirement for energy production systems. There is a whole section on photovoltaic system requirements that does not mention voltage drop. Plus the industry standard design guidelines would be much less than 5% anyway. So this is not something you need to worry about.

    Worry much more about having an AC voltage drop above 2.5% or so. That can cost you big bucks when you have to replace all that conductor and conduit because the PV inverters keep shutting down under maximum production because the utility is supplying at the high end of the ANSI voltage range. In my experience 600 ft @ 480V 3ph is about as far as you can get with a reasonable conductor size even when paralleling circuits and keeping the voltage drop low.

  9. #9
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    790
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MJennings View Post
    YThe spec sheet shows "AC Output Voltage Minimum-Nominal-Maximum(1) (L-L) 422.5 - 480 - 529 Vac". So it looks like even the worst case scenario as far as VD will still keep the voltage within the manufacturers parameters. Not ideal but doable, yeah?
    The ANSI B range upper end is 508V. That means you get at most 11V of voltage drop to work with before you hit 529V . Based on a nominal voltage of 480V that gives you 2.29% voltage drop. Even the less conservative A range upper limit is 504V allowing up to a 3.12% voltage drop. Get even close to these and you are rolling the dice on having to maybe replace all the AC conductor and conduit. Have a fat reserve fund if you want to play that game on a 1000 ft run.

  10. #10
    Join Date
    May 2011
    Posts
    5,463
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by MJennings View Post
    Your 177A figure is probably accurate in terms of actual production but we're using two SE100k SolarEdge inverters that have a max output rating of 120A each. Multiplied by 1.25 that puts it at 150A each.

    https://www.solaredge.com/sites/defa...tasheet_na.pdf

    The spec sheet shows "AC Output Voltage Minimum-Nominal-Maximum(1) (L-L) 422.5 - 480 - 529 Vac". So it looks like even the worst case scenario as far as VD will still keep the voltage within the manufacturers parameters. Not ideal but doable, yeah?
    I can't imagine why you're oversizing your inverters so much, but that's irrelevant. There's no code requirement that would have you use 125% of the inverter output for a voltage drop calculation.