User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 18
Thread: Wiring pole barn for client in MI
  1. #1
    Join Date
    May 2019
    Michigan
    Posts
    4
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hello. I'm wiring a pole barn for a client in Michigan using PVC conduit from the home to the pole barn. The way I interpret 250.122 is that the barn should not be bonded and should not have a separate ground rod but rather the ground in the barn should be run back to the home where it is bonded in the panel and there are ground rods.
    Is this correct?
  2. #2
    Join Date
    Dec 2010
    Tennessee NEC:2017
    Posts
    5,317
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by wacnstac View Post
    Is this correct?
    First of all, 250.122 is for EGC (Equipment Grounding Conductors), which you should run in the feed with the other conductors.
    The panel in the barn would be a subpanel and you're correct in that it should not be bonded, meaning the neutral (grounded conductor) is not bonded to the EGC or panel cabinet.
    You DO need two ground rods (if that's what you are using for a GEC [grounding electrode conductor]). You connect the GEC from the rods to the EGC bar and not the neutral bar.
    Welcome to the forum!
    If you aim at nothing, you will hit it every time!
  3. #3
    Join Date
    May 2019
    Michigan
    Posts
    4
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Little Bill View Post
    Sorry, typo on the NEC section number. There are two ground rods at the house connected to the ground bar at the main panel which is bonded. Does this count as the GEC for the non-bonded ground (at pole barn) running back to the house from the pole barn (and tied into the ground bar at the house)? Or does the non-bonded ground bar at the pole barn need to be connected to two ground rods at the pole barn? This is where the confusion for me always starts when using non metalic feeder conduit to the barn.
  4. #4
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    25,718
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The barn requires its own GES; a metallic conduit does not change this.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  5. #5
    Join Date
    Dec 2010
    Tennessee NEC:2017
    Posts
    5,317
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I said you needed the GES/ground rods (in red above). I did fail to say at the barn but that's what we were talking about and assumed you knew what I meant.
    As Larry said, you need a GES at both the house and the barn and has nothing to do with whether you run a wire EGC or metal conduit.
  6. #6
    Join Date
    May 2019
    Michigan
    Posts
    4
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    10/4 and thanks.
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,565
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What are you running to the "barn"? If it is a multiwire branch circuit you are not required to install a grounding electrode at the second structure. If it is feeder or service you must install a grounding electrode at the second structure. If it is service - you bond the grounded conductor like you do at any other service, since you said you are supplying it from the house it is likely either MWBC or a feeder though. If it is a feeder you still need a grounding electrode at the second structure but you tie it to the EGC instead of the grounded conductor (neutral).
    I live for today, I'm just a day behind.
  8. #8
    Join Date
    May 2019
    Michigan
    Posts
    4
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    It is what I would consider a feeder (feeding a multicircuit box in the barn). 4 wires underground (hot, hot, neutral, and ground all tied into the same at the house). I have the same understanding, that the pole barn needs its own grounding electrode tied into EGC which in this case is not bonded to neutral in the barn.
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,565
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    That is correct.
  10. #10
    Join Date
    Sep 2005
    Greenville SC
    Posts
    791
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Let's raise the ugly UFER head again ... new pole barn, maybe concrete floor on grade with steel, if so that must be the GEC connection.